SMT750I , Questions before purchase

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT750I , Questions before purchase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
13
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

SMT750I , Questions before purchase

Hello, i am in the process of purchasing a new UPS, exactly the one mentioned in the topic SMT750I, but before, i need to know:

Does it have any fan? this is the most important thing i need to be sure, as i need a 100% silent unit.

Can the display be turned off?

I read that at standby, this unit consumes around to 60w, is this true? even when nothing is drawing power?

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

  • SMT750/SMT750I units do not have a fan.
  • Recent firmware revisions have introduced the ability to turn the display off. You'd need to enable the feature in the LCD menu and I think it goes off after a few minutes or something like that. I
  • 60W is high. Keep in mind, this answer depends on if the battery is fully charged or not. The battery charger wattage is 49W so if the battery is fully discharged with no load, it'd draw at least that most likely. We also have a UPS efficiency calculator (located here -> http://www.apc.com/tool/?tt=5) and you can look up your UPS model there and compare the model to itself. If you do that, then you'll get a graph on the right where you can look at UPS system losses and you can show it at 0% load. If I do that, I see 8W is the answer. So, with no load and battery fully charged, the UPS power consumption would be 8W.

1430_smt.jpg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

Hello, i am in the process of purchasing a new UPS, exactly the one mentioned in the topic SMT750I, but before, i need to know:

Does it have any fan? this is the most important thing i need to be sure, as i need a 100% silent unit.

Can the display be turned off?

I read that at standby, this unit consumes around to 60w, is this true? even when nothing is drawing power?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:56 AM . Last Modified: ‎2024-03-12 04:52 AM

  • SMT750/SMT750I units do not have a fan.
  • Recent firmware revisions have introduced the ability to turn the display off. You'd need to enable the feature in the LCD menu and I think it goes off after a few minutes or something like that. I
  • 60W is high. Keep in mind, this answer depends on if the battery is fully charged or not. The battery charger wattage is 49W so if the battery is fully discharged with no load, it'd draw at least that most likely. We also have a UPS efficiency calculator (located here -> http://www.apc.com/tool/?tt=5) and you can look up your UPS model there and compare the model to itself. If you do that, then you'll get a graph on the right where you can look at UPS system losses and you can show it at 0% load. If I do that, I see 8W is the answer. So, with no load and battery fully charged, the UPS power consumption would be 8W.

1430_smt.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Yes, Line Interactive Smart UPS like this one have AVR. I see the answer in this user's guide -> http://www.apcmedia.com/salestools/SCON-7NBSEM/SCON-7NBSEM_R5_EN.pdf Refer to PDF page 9.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Sorry, i only see the threshold for battery transfer, there is no mention of at what voltage AVR trims or boosts..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Sorry, my error. The voltage transfer ranges listed there are the only ones that you can adjust via the LCD or the NMC so I had that on the brain. The AVR transfer points I don't have readily accessible unfortunately..it also may change between firmware revisions.

Reply

Link copied. Please paste this link to share this article on your social media post.

hkpolice_apc
Ensign hkpolice_apc
Ensign

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

I have this unit running in my house (120v version) and it's NOT 100% silent. While there are no running fans, the battery charger and or transformer emits buzzing electrical noise all the time. Depending on how quiet the ambient noise is, you might not be able to hear it like if there's a desktop running nearby, but if it's dead quiet at night and you're trying to sleep you will notice it. I also have an SMT1500 unit and it makes a much louder buzzing noise noticeable much further away. This seems to be the norm for these new SMT unit whereas the older SUA units are generally quieter.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Ok, while looking at the shop, i seen bigger unit, SMT1000I , can you please verify if this one also comes fanless?

Thanks hkpolice, i'll be aware of it when i get the unit, hope it does not end bothering too much...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Anything larger than a 750 typically has a fan. SMT1000I has a fan.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Okay, will definitely go for the 750 then.

I can't find the transfer time ms, do you know it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Depends on the sensitivity. If its at high (default), you'll see 2-4ms, 4-6ms for medium, and 6-8ms at low sensitivity. The more THD (total harmonic distortion) on the input, the longer the transfer time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Finally received the unit, everything seems ok, only thing i noticed, is that when it's on battery, with an average amount of load, it emmits a sound like water bubbles, like brbrbrbrbrbr... does this is normal?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

You'll hear some type of noise while the inverter is operating but I can't say it sounds like water bubbles to me..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Maybe water bubbles was not the correct word, more like some type of electric noise...

It fluctuates, when there is no load, it's almost silent, but when there is 150 or more watts, it's more pronounced..

I'll try to make a video as soon as i can get a mic, just to make sure it's normal...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore