APC 2200 - error after overstrain 6 LEDs flashing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 2200 - error after overstrain 6 LEDs flashing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
5
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

APC 2200 - error after overstrain 6 LEDs flashing

Hello, on my UPC after overstrain died. Then 6 LEDs flashing and UPS donť switch to battery mode. The nUPC canť turn on normally. I have to disconnect all devices and from electricity and after then I can turn on it. I dont know if I have to buy new battery, because when I mesured voltage on load on batteries, all of then are OK. If I switch UPS on battery normally UPC is OK. What can be wrong with UPS?

UPS is situated in server room on the top of the hill and when is bad weather with the storms, there is ussually overstrain because of flash from storm.

Thank you for your advice.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

I would contact local APC support in your region to verify all of your options. I can only speak for the USA and what we would do here.

We have a certified repair vendor we work with here that I'd suggest and your region may have the same. If the UPS is under warranty, a replacement could be provided via APC under warranty. Another option for a replacement may be to trade in your old UPS for credit towards a new one.

This is not an issue that is intended to be serviceable-able by a user unfortunately.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Could you clarify what you mean by overstrain? I am not sure it is coming across correctly in English to me to describe what you mean. I am guessing you may mean overload in relation to maxing out the the UPS capacity?

Center 6 LEDs flashing indicates a relay weld. This would not indicate a new battery in any situation. You'd want to look at repair if offered in your region or a trade in for the UPS if it is not under warranty.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

Overstrain means high volatage than 230 V.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:57 AM . Last Modified: ‎2024-03-12 04:52 AM

OK, so overvoltage is what I would call that or high voltage is appropriate too. This high voltagewould probably be trimmed by the Automatic Voltage Regulation (AVR) function of your UPS and if that is happening very often, the relay could've welded from frequent use and/or high current. Center 6 LEDs do refer to AVR relay weld specifically.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

Thanks, and what to do with it? To repait AVR  or what ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:58 AM . Last Modified: ‎2024-03-12 04:51 AM

I would contact local APC support in your region to verify all of your options. I can only speak for the USA and what we would do here.

We have a certified repair vendor we work with here that I'd suggest and your region may have the same. If the UPS is under warranty, a replacement could be provided via APC under warranty. Another option for a replacement may be to trade in your old UPS for credit towards a new one.

This is not an issue that is intended to be serviceable-able by a user unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore