UPS 1000 is going in Battery Mode for only seconds

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS 1000 is going in Battery Mode for only seconds
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
5
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

UPS 1000 is going in Battery Mode for only seconds

Hiwe have a APC 1000 on a Synology 3018xs. In Synology Setttings i adjust the Synology to remain 15 minutes in battery and then switch to save mode.

The APC 1000 was installed without changing any settings.

Problem is.

Every day or two on different times the Synology write me a email that says it goes to battery mode.

Then on the same minute another email comes that said it goes back to power mode.

Why is this? Ps live in Germany here.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

Hi Oli - 

You are experiencing an intermittent power issue. If you are using Powerchute Business Edition you can review the logs to see if it is a voltage disturbance or perhaps related to distortion or frequency drift. You can adjust the sensitivity of the UPS and voltage transfer points via Powerchute Business Edition. Alternately if you want to adjust via the LCD screen on the UPS you can use the steps outlined on page 7 of the users manual, which you can download here: http://www.apc.com/salestools/AHUG-9D8BRK/AHUG-9D8BRK_R2_EN.pdf

Thanks 

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

Hi Oli,

Which particular UPS model are you using? APC has several different 1kVA models so I just want to see if this is a UPS that is capable of logging input data.

APC UPS models are designed to perform a self test (battery test) which results in a momentary transfer to battery after which the UPS transfers back to online mode. A self test is typically performed every time the UPS is turned on,or every 7 or 14 days, depending on the configuration, but would not normally be performed automatically every day or two.

Input conditions such as a momentary voltage spike or sag could also result in the UPS transferring to battery for a short time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:48 AM . Last Modified: ‎2024-03-17 11:48 PM

Thanks for the answer. As I wrote we have the APC smart USV 1000

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

Hi,

You will find the exact model number of the UPS on the bar code sticker. 

1vhb29mCr6hubm4AuvduLw%3D%3D.png1vhb29mCr6hubm4AuvduLw%3D%3D.png

The bar code sticker will be on the back of the unit or possible behind the front bezel of a rack mount unit. 

If the Smart-UPS is a SMT, SMX, or SRT 1000 those units will display information as to why the UPS switched to battery via the LCD penal. Press the Esc key then the enter key nd using the up or down arrow scroll to Logs. Press enter to open the logs and you will find Xfer events, and Fault Events. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

Dont have access yet but its this one

APC Smart-UPS SMC - Unterbrechungsfreie Stromversorgung 1.000VA - SMC1000I - Line Interactive, AVR, 8 Ausgänge IEC-C13, Shutdown Software https://www.amazon.de/dp/B00DZIDRC2/ref=cm_sw_r_cp_tai_eLuKBbR9K1FJQ

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

0 Likes
0
1744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:49 AM . Last Modified: ‎2024-03-17 11:48 PM

Hi Oli - 

You are experiencing an intermittent power issue. If you are using Powerchute Business Edition you can review the logs to see if it is a voltage disturbance or perhaps related to distortion or frequency drift. You can adjust the sensitivity of the UPS and voltage transfer points via Powerchute Business Edition. Alternately if you want to adjust via the LCD screen on the UPS you can use the steps outlined on page 7 of the users manual, which you can download here: http://www.apc.com/salestools/AHUG-9D8BRK/AHUG-9D8BRK_R2_EN.pdf

Thanks 

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore