Trigger controlled shutdown with PCNS 2.2.3

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Trigger controlled shutdown with PCNS 2.2.3
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
4
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Trigger controlled shutdown with PCNS 2.2.3

Hello together,

I have some questions concerning the subject above:

I'm currently testing with a SmartUPS 3000 and PCNS.

As I have learned one can configure the Low Battery Duration to x minutes in order to send a low Battery Signal when this remaining time is reached. And one can also configure the PCNS-Client to react on the "On Battery Signal" with certain events like shutting down the operating system etc. Using this Option seems a little bit unsafe to me, because the remainig time until the battery will be discharged is very variable. One can't assume that the runtime shown in PCNS is alway correct.

Therefore my question is: Can't I connect the shutdown of the Client to the Low Battery Duration (Low Battery Signal)? So that I can start my shutdown procedures for the PCNS-Client (e. g. I set a Low Battery Duration of 10 min) when this time begins. So that the shutdown process can be triggered within these 10 minutes?

Please forgive me, for my bad english 😉

Greetings,

Jan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Thanks for the informations!

Wish u a nice weekend!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Even if you configure the "on battery" shutdown event for an excess number of minutes, the system will still shutdown on "low battery" as a safety net.

Generally the "on battery" option is used in instances where sequential shutdown is needed or to shutdown certain servers to give others a bit more runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Nice to know,

so if I just wanted my server to start a command file, when the low battery event occurs (set by low battery duration) I have to configure the Command File Execution under the "Configure Shutdown" Tab in the PCNS-webinterface of my server. A configuration of a certain event in addition to "Low Battery Duration" to trigger the shutdown is not needed?

Greetings,

Jan

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
0
607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Jan,

If you just have the default setup for shutdown @ low battery, you don't need to configure anything for an event.

If you were controlling shutdown based on a specific event, it would still use the overall setup of the shutdown configuration to execute the command file. You're just telling it to shutdown for a specific event occurrance instead of Low Battery Signal.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

0 Likes
0
608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:28 AM . Last Modified: ‎2024-03-08 02:30 AM

Thanks for the informations!

Wish u a nice weekend!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of