Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
hi,
I have a SU3000RMXL3U UPS and would like to plug it into a portable gas generator in case of extended blackouts.
Problem is the UPS has a L5-30P plug but the generator has a L14-30R receptacle.
Does anyone know if there is an adapter I can purchase?
Does anyone have any experience using a portable generator with a UPS?
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
How big is the generator? Generators should be 1.5x the size of the load that will be pulled by the UPS.
This kbase talks about one of the common problem in using generators with our UPSs:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7354&p_created=1135178608&p...
If the output power of the generator is fairly clean and accepted by the UPS then this product should help.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7583
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
How big is the generator? Generators should be 1.5x the size of the load that will be pulled by the UPS.
This kbase talks about one of the common problem in using generators with our UPSs:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7354&p_created=1135178608&p...
If the output power of the generator is fairly clean and accepted by the UPS then this product should help.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7583
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.