hi,
I have a SU3000RMXL3U UPS and would like to plug it into a portable gas generator in case of extended blackouts.
Problem is the UPS has a L5-30P plug but the generator has a L14-30R receptacle.
Does anyone know if there is an adapter I can purchase?
Does anyone have any experience using a portable generator with a UPS?
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
How big is the generator? Generators should be 1.5x the size of the load that will be pulled by the UPS.
This kbase talks about one of the common problem in using generators with our UPSs:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7354&p_created=1135178608&p...
If the output power of the generator is fairly clean and accepted by the UPS then this product should help.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7583
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:28 AM . Last Modified: 2024-03-08 02:31 AM
How big is the generator? Generators should be 1.5x the size of the load that will be pulled by the UPS.
This kbase talks about one of the common problem in using generators with our UPSs:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7354&p_created=1135178608&p...
If the output power of the generator is fairly clean and accepted by the UPS then this product should help.
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7583