Transfer time specifications of the Symmetra MW
Hello,
We are looking for the transfer time specifications of the Symmetra MW.
We need to know the transfer times (in ms) for both the internal bypass and external bypass units for the following actions:
Bypass to battery/inverter Battery/inverter to Bypass
Some UPS maintenance was being done and when the unit was switched from bypass to normal operation some equipment connected to the UPS lost power.
We are trying to determine if the time it takes the Symmetra MW to switch between bypass and inverter/battery is less / more than the time our equipment power supplies stay energized once there is a loss of power.