The system needs to reboot for a configuration change to take effect.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The system needs to reboot for a configuration change to take effect.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
5
13576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

The system needs to reboot for a configuration change to take effect.

I have a AP8930 PDU and am changing the IP number. It says the system needs to reboot for a configuration change to take effect. If I reboot it, will it kill the outlets on the PDU or just reboot the interface?

I can't seem to find a manual for this particular PDU. Does anyone have a link to one?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • captstent
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

The hysteresis setting was introduced to prevent the problem of a unit continually sending out new email alerts. Say you have a threshold of 75 degrees. The temperature goes above 75, you get an "alarm" message. It goes back to 75, you get an "alarm cleared" message. If the temperature is fluctuating slightly right around the alarm threshold, you can get many of these messages. With hysteresis, the temperature needs to drop back down by the number of hysteresis degrees (for example, to 73 degrees if you set it to 2 degrees) before the unit considers the alarm cleared. Normally the unit will send out "reminder" messages if a violation still exists. You can tune the frequency and delay of those messages as well.

Technical point: As the unit allows temperatures to be set in either degrees C or degrees F, and the actual values read from the probe are voltages that need to be converted to digital numbers, there is a bit of unavoidable "slop" in the conversion process. I normally suggest adding 1 degree F to whatever you think the hysteresis value should be, to avoid nuisance messages.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hi Bob,

On any of these APC Rack PDUs, under normal circumstances rebooting the management interface will not affect the outlets or cause them to reboot. I was under the impression as well if you log out or your session expires (and no other users are logged in), it will also automatically do the reboot for you to apply the setting rather than you needing to specifically command it to reboot.

Side note: I would only urge caution to any user coming across this post that if you were going to reboot but your Rack PDU has concerning alarms like lost internal communication alarms because then in these rare potential fault scenarios, the outlets may reboot depending on what the failure is.

Try this link for all the documentation on this PDU: http://www.apc.com/shop/us/en/products/Rack-PDU-2G-Switched-ZeroU-20A-100-120V-24-5-20R/P-AP8930#doc... (you may need to scroll down a little bit and specifically click on the documentation tab to see the documents listed)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

I appreciate you help and information.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

So then clicking the "Apply" button doesn't reboot it? I'll look in the documentation on how to reboot it.

If I can, you seem knowledgeable about these things, we have a temperature sensor plugged into this unit.

It is in a small room and the temperature swings from 72-77 over the cooling cycle. We kept getting alarms

for high temperature so I adjusted the set point on the alarm and moved the sensor away from the back of a

server that had been installed. Can you explain to me in simple terms what the Hysteresis is and if I need a small number

or big number? My assumption was that it was like giving me extra time for the temperature to come down so I could avoid

the constant alarms we were getting.

Max (Critical): °F [32 to 140]
High (Warning): °F [32 to 140]
Hysteresis: °F [0 to 18]
Alarm Generation: Enable
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hi Bob,

Correct, you have to specifically give a reboot command. I think also if it has pending changes, when the last user logs off the system, it will reboot after the session ends.

To command a reboot via the command line, you can issue the reboot command and follow the prompts to confirm that. Though the web UI, go to Control->Network->Reset/Reboot and then the radio button defaults to the correct option - "Reboot Management Interface." Then, apply that, which I think it asks you to confirm and you click Apply a second time. Then, the reboot will happen and it takes about 20-30 seconds usually.

On your other question, hysteresis is like a buffer. It is the difference between the particular threshold violation and the clearing point. I usually suggest anything between 3-5º typically. I think you have the right idea of what it is for but maybe you need to set it to 5 or 6º if the temperature variation isn't something you can tighten up or avoid with cooling adjustments, like you did with moving it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
13573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

The hysteresis setting was introduced to prevent the problem of a unit continually sending out new email alerts. Say you have a threshold of 75 degrees. The temperature goes above 75, you get an "alarm" message. It goes back to 75, you get an "alarm cleared" message. If the temperature is fluctuating slightly right around the alarm threshold, you can get many of these messages. With hysteresis, the temperature needs to drop back down by the number of hysteresis degrees (for example, to 73 degrees if you set it to 2 degrees) before the unit considers the alarm cleared. Normally the unit will send out "reminder" messages if a violation still exists. You can tune the frequency and delay of those messages as well.

Technical point: As the unit allows temperatures to be set in either degrees C or degrees F, and the actual values read from the probe are voltages that need to be converted to digital numbers, there is a bit of unavoidable "slop" in the conversion process. I normally suggest adding 1 degree F to whatever you think the hysteresis value should be, to avoid nuisance messages.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of