New battery in SMT2200RM2U showing low capacity

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • New battery in SMT2200RM2U showing low capacity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
14
2768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

New battery in SMT2200RM2U showing low capacity

Last week I replaced the battery cartridge in the above model UPS. The replacement was a new APC battery. After installation I set the battery install date via the front interface. The battery then showed 100% capacity, but slowly began counting down. It was at 97% after a few minutes, but I left it thinking it might straighten itself out overnight. Well yesterday it ran and passed it's first scheduled self-test. The resulting log message for this self-test is confusing. It says "UPS: passed via failed a self-test." Even though that is confusing my main concern is the battery capacity. It has now been 7 days since installing the new battery (no fail over to battery has occurred either) yet the UPS is reporting 35% battery capacity.

UPS Output Watts - 18%

Input/Output - 118 VAC

Battery Runtime Remaining: 23min

Is there something else that needs to be done?

(I am running a network management card).

Resetting or rebooting the UPS would be a last resort as it is running a distribution switch in our nearly 24hr environment.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • battery
  • capacity
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hi,

It is ID18 so it looks like you can go to UPS 09.3 as outlined here in the chart towards the bottom -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737 

You can download the UPS 09.3 file from there and then use your Network Management Card to push the firmware to the UPS as I might have mentioned - instructions are here to do that (http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA170679). You just need to make sure that because you turn the power output off and have to manually turn it back on, that you're not powering your Network Management Card's network connection that way. 

I can look at the logs you can get from the About->Support in the v6.2.0 web UI. You need to press generate logs and then download them and provide me the .tar file you'll get.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

Could you provide the log dump via About->Support in the web interface to review?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:59 PM

I'm sorry I dont have that option under About. Just the serial, firmware, and manufacture date (09/2011)

I don't see any support options. This may be an old interface. 

This is a UPS network management card 2

The very bottom left says "2009, Schneider Electric. All rights reserved"

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

Oh, ok, yes, it is probably an earlier version. I was referring to v6.X.X firmware which is current and it sounds like you have v5.X.X.

Here are instructions on retrieving log files on all versions -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131

I am looking for event.txt, data.txt, and config.ini.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

Firmware Revision - UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0

I don't see an ID number.

I will evaluate and discus with my mgr regarding upgrading. Is there any risk at all that the UPS could reboot or lose power to the outlets on the back during the upgrade? If there is even the smallest risk we will have to get further approval since an outage is possible.

Just to be clear...is it possible to upgrade our current card to 6.x.x ?

This is interesting...just a few hours ago we had a brief site wide brown-out. The UPS is reporting it was on battery power for the duration of 1 second. The battery capacity is now at 41% (27min runtime).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

What did you see under UPS->About for firmware?

And no, when you upgrade the Network Management Card, it does not affect the UPS or whatever type of device it is in. Only the Network Management Card will reboot its management interface. However, if you have to upgrade your SMT2200RM2U UPS some day, that procedure does require the UPS output to be turned off in order to perform the upgrade.

And yes, any AP9630/31 when used with a Smart-UPS can be upgraded to v6.X.X. There are some products out there that use AP9630/31 that do not yet have an application at the v6.X.X revision level but yours does and that is what I attached earlier.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

Here is the entire About page followed by the General tab under administration.

 

About UPS
 
Model: Smart-UPS 2200
Serial Number: IS1139002069
Firmware Revision: UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0
Manufacture Date: 09/21/2011
 
Apparent Power Rating: 2200 VA
Real Power Rating: 1980 W

 

-------- Administration > General ----------


Hardware Factory
  
Model Number: AP9630
Serial Number: ZA1132014983
Hardware Revision: 05
Manufacture Date: 08/03/2011
MAC Address: 00 C0 B7 5C 17 19
Management Uptime: 34 Days 19 Hours 27 Minutes
 
     
  Application Module
  
Name: sumx
Version: v5.1.3
Date: May 4 2010
Time: 14:06:35
 
     
  APC OS (AOS)
  
Name: aos
Version: v5.1.3
Date: May 4 2010
Time: 13:55:26
 
    
  
APC Boot Monitor
  
Name: bootmon
Version: v1.0.1
Date: Aug 3 2009
Time: 16:30:40

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

Hi again,

OK, yes, there is an update available for your UPS as well. And I think the lack of ID was also addressed in a newer version of the Network Management Card firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Just to be clear...the EXE's and instructional link you posted earlier is to upgrade the firmware on the Network Management Card?

We may consider upgrading the UPS firmware too.  I just tried looking up the firmware for just the UPS and it was quite overwhelming. There seems to be so much available. Can you post the link to the correct firmware & tutorial for upgrading our UPS?

Thanks for all you help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hi - yes, I am confirming the .exe's for firmware I gave you are Network Management Card only.

For upgrading your UPS, this is the best resource -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737

I was looking for the "ID" on the UPS because that makes the UPS upgrade procedure a lot less overwhelming smile so if you update the Network Management Card first, we could get that hopefully and then work on determining the available ways to update your UPS - some can do it via USB, serial, and via the Network Management Card (it can push a file to the UPS if the UPS supports it).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

For the network mgmt card...Can I upgrade directly to 6.x.x from my current firmware, or do I need to update to v5.1.7 first?)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

You can go straight to v6.X.X without issue. This may help you just as some guidance -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA167693

Furthermore, do you use HTTPS secure web access? It doesn't sound like you do but we'll be releasing AOS v6.2.1/sumx application for Smart-UPS this week to fix this issue -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA238115 but that is the only benefit it has over v6.2.0. If you use HTTPS, you could wait a day or two until it is on the website. If you don't use HTTPS, go ahead with v6.2.0 if you want to do it now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

I updated the NMC2 firmware yesterday. I can now view the ID you were talking about. The battery percentage currently shows 42% (28min runtime) with an output load of 17 percent.

Can you now advise me what firmware I should upgrade the UPS to?

Firmware Revision: UPS 06.5 (ID18)
Manufacture Date: 09/21/2011

 thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Also let me know if there are now logs available in v6.2.0 you might be interested in viewing.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
2767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hi,

It is ID18 so it looks like you can go to UPS 09.3 as outlined here in the chart towards the bottom -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737 

You can download the UPS 09.3 file from there and then use your Network Management Card to push the firmware to the UPS as I might have mentioned - instructions are here to do that (http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA170679). You just need to make sure that because you turn the power output off and have to manually turn it back on, that you're not powering your Network Management Card's network connection that way. 

I can look at the logs you can get from the About->Support in the v6.2.0 web UI. You need to press generate logs and then download them and provide me the .tar file you'll get.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore