Remote On-Off & Status for UNIFLAIR TDCV Units

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Remote On-Off & Status for UNIFLAIR TDCV Units
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
6
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:42 PM . Last Modified: ‎2024-03-18 11:58 PM

Remote On-Off & Status for UNIFLAIR TDCV Units

Hello Everyone,

We are installing some TDCV Cooling Units in one of our Data Center Project where all these units will be controlled by a centralized Automation Controller, though during the configuration we are facing following issues and we would really appreciate if someone can guide us in resolving these issues.

  1. Is there any built-in ModBus RTU Port available in TDCV Units or we must  use external Serial Cards with to integrate the units with our Automation Controller (supports RTU Connectivity).
  2. Is there any Dry-Contact available in TDCV which can provide us status of the system means if the system is in working condition it provide us one state and whenever the system is off (due to any malfunctioning or alarm) it provides us a different state.
  3. We want to control the units through a remote command and I believe DI-2,4 or 6 can be used for this purpose, however I just want to confirm if we have to apply 24VDC/AC to turn on the units through remote command or if the voltage should be applied to turn-off the running system. Moreover, if we want to use the system in Auto-Mode with Remote On/off enabled then do we have to enable Manual Override as well?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • bms
  • control
  • crah
  • modbus
  • tdcv
  • uniflair
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hello.

Under the hardware configuration screen try setting the FS run delay to 30 seconds. This should allow enough time for the other pump to get up to speed before the flow alarm is triggered. If this does not work i would recommend calling into your local technical support to work through this issue further. 

Thank you

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

Hello Waleed.

The TDCV cooling unit will need a serial card to use modbus RTU. The Part number for the card is ACAC76123 (RS485). There is also a RS232 for modems ACAC76125.

There are two output dry contacts that can be configured to switch state when an alarm is on the unit.  C7 and C8 (J14 and J15) on the main board. The alarms will need to be set up under the settings and alarm relay selection section. This will not tell you if the unit is off but only if there is an alarm on the unit. You can choose which alarms change the state of the contact.

For the remote off, you are correct that DI-2,4 or 6 can be configured to turn off the unit. The unit will provide the 24 volts for the shutdown. Do not put an external 24 volt source on the inputs. This will fry the transformers in the unit. Connect a dry contact to the unit that is Normally Closed.  The unit is expecting to see the 24v at the input while the unit is running. A loss of the 24v will shut the unit down. Do not enable the manual override. All you will need to do is to go into the hardware settings and set up the input you connected to, to remote on/off.

Thank you

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:58 PM

Hello,

Thanks a lot for your response.

As per my understanding of your below comment if the Digital input is set-up for remote on/off then by making it close the system will turn on and by disconnecting it system will be off, however it is not working I have set up one of the digital input and then short it by using a piece of cable but it didn't work or do we have to provide 24v from an internal  source available in the unit? 

I have also read the below faq from APC website according to which I think external has to be provided.

http://www.apc.com/us/en/faqs/FA173094/

I would really appreciate your support as this thing is delaying the complete project.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hello,

Thanks a lot for your response, last night I gave configured it for CRAH and Chillers already.

Just another quick question, we have two external pumps installed for the chiller each pump is provided with its own VFD drive, as per our sequence whenever there is a failure in one pump the other pump will start within 5 seconds and within next 25 seconds it reaches to the required flow rate but within this transition time chiller is giving flow alarm and tripping please advise if there is any way to fix this.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hello. Can you send me the model number of your chiller unit?

Thank you

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hello,

It is BREC1812.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

0 Likes
0
1415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:43 PM . Last Modified: ‎2024-03-18 11:57 PM

Hello.

Under the hardware configuration screen try setting the FS run delay to 30 seconds. This should allow enough time for the other pump to get up to speed before the flow alarm is triggered. If this does not work i would recommend calling into your local technical support to work through this issue further. 

Thank you

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of