Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
The explanation is not clear for me
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0901:59 AM. Last Modified: 2024-02-1411:22 PM
The explanation is not clear for me
Hi,
i have an UPS connected with my esxi host with the nmc2. Running 3 vm's on it.
I did a test and the ups went off after 25 min. But some of the vm's werent shutdown correctly.
I checked the powerchute settings, I can't figure out in the settings what I need.
I want it to run 10 minutes and then the virtual machines start shutting down one by one. If I get power within 10 minutes, all is good and nothing should happen with the vm's.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0901:59 AM. Last Modified: 2024-02-1411:22 PM
Hi,
To configure PowerChute Network Shutdown to shutdown the OS after UPS has run on battery for 10 minutes open the PowerChute web page and go to Configure Events and select UPS on Battery - Shutdown. Click Enable Shutdown and enter 600 second delay. Then click apply. After the UPS has been running on battery for 10 minutes the host will be commanded down.
When PowerChute is configured with a single ESXi host PowerChute sends a shutdown signal to the host. The host is responsible for shutting down the VMs. Please review Schneider electric FAQ http://www.apc.com/us/en/faqs/FA159688
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0901:59 AM. Last Modified: 2024-02-1411:22 PM
Hi,
To configure PowerChute Network Shutdown to shutdown the OS after UPS has run on battery for 10 minutes open the PowerChute web page and go to Configure Events and select UPS on Battery - Shutdown. Click Enable Shutdown and enter 600 second delay. Then click apply. After the UPS has been running on battery for 10 minutes the host will be commanded down.