Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-09 01:53 AM . Last Modified: 2024-02-14 11:23 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 01:53 AM . Last Modified: 2024-02-14 11:23 PM
I have three 40 KVA SUVT UPS synchronised through a Maintenance Bypass panel and synchronizing kit. The fault "PBUS communication fault on cable 2" is displayed on all three UPS and the fault led is illuminated. The PBUS cables seem to be OK. The UPS can synchronize. What am I suppose to do to clear this fault? How critical is this fault?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 01:53 AM . Last Modified: 2024-02-14 11:23 PM
Hi,
According to the 3 Phase support team here in North America parallel bus communication alarms can be due to poor connectivity or defective parts. A Field Service Engineer must check/verify the parallel bus cable & parallel box connections.
The recommendation is to contact local support and request the assistance of a field service engineer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 01:53 AM . Last Modified: 2024-02-14 11:23 PM
Hi,
According to the 3 Phase support team here in North America parallel bus communication alarms can be due to poor connectivity or defective parts. A Field Service Engineer must check/verify the parallel bus cable & parallel box connections.
The recommendation is to contact local support and request the assistance of a field service engineer.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.