Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Help for configuration: Single UPS and PCNS on physical host + VM shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help for configuration: Single UPS and PCNS on physical host + VM shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
stephane_apc
Crewman stephane_apc
Crewman

Posted: ‎2021-07-09 02:00 AM

0 Likes
6
535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

Help for configuration: Single UPS and PCNS on physical host + VM shutdown

This was originally posted on APC forums on 8/31/2017


Hello,

I have few questions trying to set up a Single UPS configuration with PCNS running on a physical machine and VM shutdown configured (no vApp or VM migration).

I followed the great explanations of the following blog: https://www.stevejenkins.com/blog/2013/07/howto-configure-low-battery-duration-and-pcns-to-shut-down...

I want to implement the "Time Remaining" (UPS-driven) solution.

Here is a schema from my configuration and how I understand it:

I have not configured the Event Shutdown Delay on my PCNS software.

1. Is my configuration correct?

I'm not sure because if I read the APC documentation, it seems that the Event Shutdown Delay is first used and that Low Battery Duration is then used.

2. The Maximum Required Delay doesn't moves from 2 minutes even after a NMC restart...

Thanks in advance.

Cheers

Stéphane

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This reply was originally posted by Stefano on APC forums on 5/27/2018


Hello, Bill,
Sorry, I tried, but I can't do it. Too many interacting variables. Is it too much to ask for a detailed advice where to do which setting in my relatively simple scenario? 
There is  a SmartUPS 1500 with an NMC9630, a single server (2012 core, hosting 2 virtual machines) is connected to main outlet. PCNS is installed on the host. The UPS usually has a runtime remaining of 100 minutes. My requirements are:
1. At 45 minutes of remaining run time, the PCNS or NMC should start a batch (which shuts down the virtual machines).
2. The batch takes about 1200 seconds (20 minutes).
3. After counting down these 20 Minutes the PCNS or NMC should shut down the host.
4. Four minutes after the beginning of the host shutdown, the UPS should switch off server and itself.
5. When the power flows again, the UPS should switch on itself and the server as well.
If someone thinks the remaining 21 minutes (45 - 20 - 4) are a waste: My intention is to have a safety buffer in the case that the battery suffers from old age and will not survive the calculated remaining runtime.
Thank you very much if you (or someone else) could configure this process as an example.
Greetings,
Stefano

See Answer In Context

Reply
Share
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This reply was originally posted by Bill on APC forums on 8/31/2017


Hi,

What is the model of the UPS, where is vCenter installed, and how many host are being powered down? 

Reply
Share
stephane_apc
Crewman stephane_apc
Crewman

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This was originally posted on APC forums on 8/31/2017


UPS model is Smart-UPS SRT 5000

vCenter is installed on a physical host (same as PCNS is installed)

I have 3 hosts (ESX) powered on Outlet group 1 (and other devices)

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This reply was originally posted by Bill on APC forums on 8/31/2017


Hi,

When you review the shutdown setting in the PCNS web interface have you selected Turn off UPS or Turn off UPS Outlet Group? Also, when you review the NMC web interface and go to Configure Shutdown is the low battery duration set for 25 minutes? If so on the same page if you select PowerChute Shutdown Parameters - Maximum Required Delay - Force negotiation and click apply the Maximum required delay should be changed to 25 minutes. 

What will happen is when the UPS runtime falls below 25 minutes the NMC will signal PCNS to start the shutdown process. PCNS will put the hosts into maintenance mode and power down the VMs based on the priority order. Then the hosts will be powered down and then the system PCNS and vCenter are running on will be power down. The UPS will wait 25 minutes plus 2 and then kill power to the outlet group or groups. 

Reply
Share
stephane_apc
Crewman stephane_apc
Crewman

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This was originally posted on APC forums on 9/1/2017


Hi,

thanks for your help, very appreciated!

No i have the default option "Do not turn off the UPS". Is the Smart-UPS SRT 5000 compatible with this option if I selected Turn off UPS?

I thought that the default behaviour of the UPS would be to be turned off (see my schema). Should I select Turn off UPS in the PCNS shutdown settings?

I have applied force negociation and the value of Maximum Required Delay is now 25 minutes...

So can you confirm that even without having set the UPS On Battery Shutdown Delay on the PCNS, my diagram is correct?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This reply was originally posted by Bill on APC forums on 9/1/2017


HI,

If you do not select Turn off UPS the UPS will power down however it will wait until the battery is drained before powering down. 

When the UPS runtime falls below 25 minutes the NMC will send a signal to PowerChute and the shutdown process as listed will start. 

The on battery event is the low battery event as reported by the NMC so there is no delay for step 1 and you have not configured a command file so step 4 is skipped.

If you look at the outlet group settings in the NMC web interface you will see that they will have a 25 minute delay based on the maximum required delay. So steps 3 through 6 will have 25 minutes to complete before power is cut to the outlet groups.

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 02:00 AM

0 Likes
0
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-09 02:00 AM

This reply was originally posted by Stefano on APC forums on 5/27/2018


Hello, Bill,
Sorry, I tried, but I can't do it. Too many interacting variables. Is it too much to ask for a detailed advice where to do which setting in my relatively simple scenario? 
There is  a SmartUPS 1500 with an NMC9630, a single server (2012 core, hosting 2 virtual machines) is connected to main outlet. PCNS is installed on the host. The UPS usually has a runtime remaining of 100 minutes. My requirements are:
1. At 45 minutes of remaining run time, the PCNS or NMC should start a batch (which shuts down the virtual machines).
2. The batch takes about 1200 seconds (20 minutes).
3. After counting down these 20 Minutes the PCNS or NMC should shut down the host.
4. Four minutes after the beginning of the host shutdown, the UPS should switch off server and itself.
5. When the power flows again, the UPS should switch on itself and the server as well.
If someone thinks the remaining 21 minutes (45 - 20 - 4) are a waste: My intention is to have a safety buffer in the case that the battery suffers from old age and will not survive the calculated remaining runtime.
Thank you very much if you (or someone else) could configure this process as an example.
Greetings,
Stefano

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc