The battery voltage exceeds the nominal battery voltage rating

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The battery voltage exceeds the nominal battery voltage rating
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
11
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

The battery voltage exceeds the nominal battery voltage rating

Can anybody help me to find out

what does this message mean?

Smart-UPS RT 5000 XL

Serial Number : ZA1125003965

error Code : 0x0154

thanks in advance

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

please take a look for additional attached in EN

now voltage rating is OK

but it happens time by time

and I have to know about reason

See Answer In Context

Attachments
event.txt.zip
data.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

Can anybody help me to find out

what does this message mean?

Smart-UPS RT 5000 XL

Serial Number : ZA1125003965

error Code : 0x0154

thanks in advance

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

This means the battery voltage in your UPS is high. Nominal refers to normal or expected and for a Smart UPS RT that you have, the nominal battery voltage is 192vDC and it floats at around 211-218vDC.

You could start by providing the logs (event.txt and data.txt) from your network management card for us to review and assist. Instructions on doing this are here ->How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

I'd also maybe suggest someone maybe do a visual check on the batteries to ensure they are not damaged then reviewing the logs will tell us more.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

please see attached files (notice that event in RU lang, I hope it is not a problem cause all error codes are international)

visually batteries is OK

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

attached files

Attachments
data.txt.zip
event.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

I can try to read the data logs at least but the event log will take me longer to go translate the event codes. Could you change web UI to english and download the logs then switch it back? embarassed

I could see in the data log at least that there was a very high battery voltage of 235VDC at one point (12.08.2013 | 14:40:07). Seems like the time frame you were referring to?

I'd have to see what could cause this type of thing but it appears to be back to normal now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

please take a look for additional attached in EN

now voltage rating is OK

but it happens time by time

and I have to know about reason

Attachments
event.txt.zip
data.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 AM . Last Modified: ‎2024-03-12 11:21 PM

Hello,

all batteries were replaced and we have no problems from that time

thanks a lot

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

Are these the original batteries? I will do some further investigation today.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

In reviewing the files further with the Smart UPS folks here, we have to believe this is an issue with the batteries themselves as there is no evidence pointing to anything else. You can try contacting your local technical support to verify warranty status to see if the UPS is under warranty and therefore, we'd be able to send you replacement batteries if that is the case. If it is not in warranty, I'd still suggest replacement batteries at this time as a first step.

The phenomenon of the high voltage on the batteries always seems to follow an on battery event of some type (power blip, UPS self test) so I also noted that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

we have 2  Smart-UPS RT 5000 XL

both of them with the same error and under warranty till okt of 2013

please notice that they use 2 additional APC Smart-UPS RT 192V Battery Packs may be the problem is in it?

how can we get replacement batteries?

thanks a lot

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

0 Likes
0
4603
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:21 PM

It could be the battery packs - anything on the battery bus. If you're under warranty, you'll need to contact your local technical support via phone or email and then they'll verify the warranty and then they'd decide which batteries they can and will replace under warranty for you. Strange that two of them have the same issue...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore