The battery is not installed properly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The battery is not installed properly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:25 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
9
6233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 PM . Last Modified: ‎2024-03-15 12:31 AM

The battery is not installed properly

Hi,

I have a Smart UPS RT 3000 model SURDT3000XLT, I've configured alerts on it and since 2-3 weeks I receive this kind of alert :

Critical - UPS: The battery is not installed properly.

and then about 1-2 minutes later a receive this one :

Informational - UPS: The battery is now installed.

It appends 1 times / weeks

Did somebody have this kind of message before and what should I do to fix it ?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM


I have just started receiving those alerts myself. On my device the "Last Battery Transfer: Unacceptable utility voltage rate of change: was displayed. I then checked the logs for that UPS and noticed that the input voltage variations is between 118.8v to 124.5v. I have four UPS devices at that location. Although these three UPS does not issue the "The battery is not installed properly" and "the battery is now installed" messages they do indicate problems with the line voltage. Two of them detects line voltage notch or spike, and the other one compensates for high input voltage.

So since all are having some sort of input voltage issue, I am going to have that office contact the building and have the electrical circuit checked back to the breaker box.
I report back the findings when the electricians to their thing.


If you find this or any other information useful please consider awarding points.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

when you see this message, do you see any LEDs on the front of the UPS? it might be too quick to catch and I imagine you aren't sitting in front of the UPS the entire day.

we just released a new firmware upgrade as well so you can check out the software and firmware section of apc.com and look for SUMX applications of 3.7.2.

also, if you get spammed with these messages and can't figure out why, you could always delay the event before sending it while we figure out whats going on with it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

All the lights are green.
Your right I'm not in front the UPS watching paint dry. Red (Bad) lights would generally issue alerts, I have never known the warning lights to blink as something happens, they usually stay until addressed. The lights are confirmed by local personel and no other alerts are generated.The batteries in my problem UPS may not be optimal which may make it generate that alert and not the others?:| but no alerts are generated.

Does anyone who had this problem have any updates on their findings?


If you find this or any other information useful please consider awarding points.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

i assume you have double checked the battery connection? and i dont suppose anyone has seen the replace battery LED blinking on the UPS at any point?

What firmware is installed on the network management card in the UPS? this is under Administration->General->About.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

I do have the same problem here with a SU3000RMi. I did a firmware update on the UPS Network Management Card (AOS v3.7.3), but that did not help.
Does anyone have new information about this and is there a chance, that a battery replacement resolves this misbehavior?
Thanks in advance...

Message was edited by: fbrem

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

i assume you verified the physical battery connections? with a non critical load, it would also be helpful to know if your UPS actually transfers to battery or does a self test - that way we could see if this is erroneous or not.

also, before you do that, you can provide your event.txt and data.txt from the NMC so that we could see if there is anything else going on in there that could be related or provide more info to diagnose the issue. instructions on obtaining event.txt and data.txt are here -> http://nam-en.apc.com/app/answers/detail/a_id/9321

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:25 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:25 PM . Last Modified: ‎2024-03-15 12:31 AM

Hi,

I have a Smart UPS RT 3000 model SURDT3000XLT, I've configured alerts on it and since 2-3 weeks I receive this kind of alert :

Critical - UPS: The battery is not installed properly.

and then about 1-2 minutes later a receive this one :

Informational - UPS: The battery is now installed.

It appends 1 times / weeks

Did somebody have this kind of message before and what should I do to fix it ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM


I have just started receiving those alerts myself. On my device the "Last Battery Transfer: Unacceptable utility voltage rate of change: was displayed. I then checked the logs for that UPS and noticed that the input voltage variations is between 118.8v to 124.5v. I have four UPS devices at that location. Although these three UPS does not issue the "The battery is not installed properly" and "the battery is now installed" messages they do indicate problems with the line voltage. Two of them detects line voltage notch or spike, and the other one compensates for high input voltage.

So since all are having some sort of input voltage issue, I am going to have that office contact the building and have the electrical circuit checked back to the breaker box.
I report back the findings when the electricians to their thing.


If you find this or any other information useful please consider awarding points.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

when you see this message, do you see any LEDs on the front of the UPS? it might be too quick to catch and I imagine you aren't sitting in front of the UPS the entire day.

we just released a new firmware upgrade as well so you can check out the software and firmware section of apc.com and look for SUMX applications of 3.7.2.

also, if you get spammed with these messages and can't figure out why, you could always delay the event before sending it while we figure out whats going on with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

All the lights are green.
Your right I'm not in front the UPS watching paint dry. Red (Bad) lights would generally issue alerts, I have never known the warning lights to blink as something happens, they usually stay until addressed. The lights are confirmed by local personel and no other alerts are generated.The batteries in my problem UPS may not be optimal which may make it generate that alert and not the others?:| but no alerts are generated.

Does anyone who had this problem have any updates on their findings?


If you find this or any other information useful please consider awarding points.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

i assume you have double checked the battery connection? and i dont suppose anyone has seen the replace battery LED blinking on the UPS at any point?

What firmware is installed on the network management card in the UPS? this is under Administration->General->About.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

Yes, I've double check the battery connection, I also change the battery (I have another ups same model) and I still have the same message.

Here is what I have in About :

Hardware Factory
Model Number: AP9617
Serial Number: NA0803013982
Hardware Revision: A10
Manufacture Date: 01/16/2008
MAC Address: 00 C0 B7 CB 16 C8
Management Uptime: 21 Days 4 Hours 45 Minutes

Application Module
Name: sumx
Version: v3.5.5
Date: 05/24/2007
Time: 16:14:52

APC OS (AOS)
Name: aos
Version: v3.5.5
Date: 05/24/2007
Time: 15:44:22

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

ok at this point, i'd recommend upgrading the firmware on the network management card since it seems to be erroneous at this point since we have checked the physical causes.

the latest firmware is SUMX 3.5.8/AOS 3.6.1. you can upgrade this with no disruption to the load on the UPS, then we can monitor it to see if has cleared itself up.

[you can download the firmware from this link|http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=SFSUMX358&tab=Software] and download the SFSUMX358 part number.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

I do have the same problem here with a SU3000RMi. I did a firmware update on the UPS Network Management Card (AOS v3.7.3), but that did not help.
Does anyone have new information about this and is there a chance, that a battery replacement resolves this misbehavior?
Thanks in advance...

Message was edited by: fbrem

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

0 Likes
0
6231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:26 PM . Last Modified: ‎2024-03-15 12:31 AM

i assume you verified the physical battery connections? with a non critical load, it would also be helpful to know if your UPS actually transfers to battery or does a self test - that way we could see if this is erroneous or not.

also, before you do that, you can provide your event.txt and data.txt from the NMC so that we could see if there is anything else going on in there that could be related or provide more info to diagnose the issue. instructions on obtaining event.txt and data.txt are here -> http://nam-en.apc.com/app/answers/detail/a_id/9321

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore