The Application Is Incompatible With This APC OS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The Application Is Incompatible With This APC OS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
5
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

The Application Is Incompatible With This APC OS

I received the error in the subject line after configuring the email server to use gmail. I telnetted into the device and ran the "resetToDef -p keepip" command and after rebooting I was able to log into the web interface again.

Ideally I would like to configure the system to use my office 365 smtp server but I believe that is still unavailable.  I have the model AP9631 in production and it is using the 6.4.0 version of the application module, 6.4.0 version of the APC OS and 1.0.8 of the APC boot monitor.  How can I configure this device to send email alerts using either office 365 or gmail?  Has this issue been resolved yet?

What I see in my logs after changing the email server to gmail and attempting an email test is:

 03/21/2017 07:06:51 System TCP/IP stack failure. Module: tfListRemove-assertion error line 132, file(.\treck\source\trlist.c)
 03/21/2017 07:06:51 System TCP/IP stack failure. Module: tfSheapFree-assertion error line 566, file(.\treck\source\trsheap.c)
 03/21/2017 07:06:51 System TCP/IP stack failure. Module: tfSheapFree-assertion error line 626, file(.\treck\source\trsheap.c)

If you need any additional information then I will be happy to provide it.

Thanks,

Chris

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • email
  • failed
  • gmail
  • office365
  • test
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

Hi Chris,

AOS (APC Operating System) 6.4.8 (or whatever version it may be renamed to) will likely be adopted by different applications throughout the rest of this year. I'd expect most applications to adopt and tentatively release by June, July, August, September depending on what else they are building in.

I think last I heard, we are looking at August/September tentatively for Symmetra application that you have because they are adding a new feature (Bacnet).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

Hi Chris,

The NMC is experiencing a TCP/IP stack failure and unable to boot so it displays the application is incompatible with the AOS. A few customers reported these exact TCP/IP stack failures using Gmail on 6.4.0 even though in-house we test with Gmail and never saw it. One customer reported they had to make a DNS change on their side and things started working again on 6.4.0. I never found out the exact details of the change. Another customer said in the next version of their app with AOS 6.4.6, the issue was resolved as well.

Specific to Offce 365, I think some people have gotten that to work but I am not 100% sure what is required and if it can be done in every environment. We will be supporting SMTP authentication with TLS 1.1 and 1.2 in our next AOS release which I think may be 6.4.8 or newer. This was one of the problems with using Office 365 for some customers I think since in current revs, we only support SSLv3 or TLS 1.0 for email authentication.

For Gmail especially, you may need to change your Gmail account's security setting and allow less secure apps to connect.

So, for Gmail at least, I suggest you try upgrading to our newest rev but I am not sure which application you're using - Smart-UPS, Symmetra, Rack PDU, etc as you just referred to application module. I can link it here if you let me know which app you need so I can confirm if AOS 6.4.6 is available for it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

Angela,

I received the warning from gmail account stating that it had blocked the traffic and I would have to lower the security setting (which I did).  I am happy to upgrade to the latest firmware if necessary.  The details for my unit are below:

Model
Symmetra LX 16000
Position
TOWER
Firmware Revision
269.514.S
Manufacture Date
11/11/13
Thanks,
Chris
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:36 PM

Hi Chris,

OK, here is the latest firmware for the AP9631 NMC itself -> ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/sy/646/apc_hw05_aos646_sy646...

Here are the release notes in case you'd like to see prior->http://www.apc.com/salestools/ARAJ-9TN74X/ARAJ-9TN74X_R4_EN.pdf 

Instructions on upgrading if you need them (refer to NMC2) -> http://www.apc.com/us/en/faqs/FA156047

Not sure if you knew but you can apply this upgrade with no affect to the UPS power output itself. This upgrade only applies to the AP9631 and its management interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

That did the trick, Angela.  I am now able to send emails through gmail.  When do you think the 6.4.8 version will be released? 

Thank you so much for the help.

 - Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
0
2115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:26 AM . Last Modified: ‎2024-03-12 11:35 PM

Hi Chris,

AOS (APC Operating System) 6.4.8 (or whatever version it may be renamed to) will likely be adopted by different applications throughout the rest of this year. I'd expect most applications to adopt and tentatively release by June, July, August, September depending on what else they are building in.

I think last I heard, we are looking at August/September tentatively for Symmetra application that you have because they are adding a new feature (Bacnet).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore