9630 NMC2 - How to get email alerts when power is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 9630 NMC2 - How to get email alerts when power is restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:24 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
3
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:24 AM . Last Modified: ‎2024-03-12 11:36 PM

9630 NMC2 - How to get email alerts when power is restored

I'm somewhat new to the 9630 NMC2. I have updated the firmware and configured email alerts and verified that they were working but I cannot find how to configure the 9630 NMC2 to send out an alert when the power is restored or the UPS is no longer on battery.

Checking the recent device events there is an event such as : 

03/15/2017 14:12:30 UPS: No longer on battery power.

How can I get email notification for these types of events?

PowerChute used to send out alerts when the power was restored but I have locations where there is not a PC, Server or VM host nearby where I can use the PowerChute Agent software along with a USB cable. I was hoping the NMC2 cards would offer similar functionality. I know that I can use third party monitoring software and make an event to send out alerts when say the input voltage is lost or restored but I was hoping the NMC2 cards would do that out of the box.

Is there something I'm missing in the NMC2 notification settings?

Any assistance or advice would be appreciated.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9630
  • email
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

Well, I did write the article way back when but off the top of my head, I did not think disabling informational alerts would disable clearing events for critical events that were indeed enabled. But, I haven't looked at in a while and I must have wrote the right thing in the article at the time laughing

I am glad you got it working.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

So If I pull the power on one of the UPSs and cause an input power event and then wait say 5-10 seconds and plug it back I should have gotten an email alert when the event cleared even if the event was under the 2 minute interval. I don't have to wait 2 minutes for it to send out a clearing event correct?

I checked my log settings and changed the URL to 0x010A and saw all of my email recipients listed there.

Just in case, I selected all events by informational, warning and severity and applied the default settings back to them for my email recipients. I saw in the article If you configured only critical events to certain recipients then the clearing events may not have been sent.

I'll give it another try and see if it sends the clearing event this time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

That must have been what it was. I must have set it to only send critical  notifications and not informational ones.

I just reset the notifications to default and it sent me an alert when the power was restored.

Everything appears to be working now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:25 AM . Last Modified: ‎2024-03-12 11:36 PM

Well, I did write the article way back when but off the top of my head, I did not think disabling informational alerts would disable clearing events for critical events that were indeed enabled. But, I haven't looked at in a while and I must have wrote the right thing in the article at the time laughing

I am glad you got it working.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore