Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

TEST REPORT for " IEC 62040-3 Performance Approval for APC SURT1000XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • TEST REPORT for " IEC 62040-3 Performance Approval for APC SURT1000XLI
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

0 Likes
8
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

TEST REPORT for " IEC 62040-3 Performance Approval for APC SURT1000XLI

Dear All,

I searched APC web pages for APC's performance test report IEC 62040-3 for SURT1000XLI units but could not find any document.

Please can someone help me with this test report.

Thanks
Saeed

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

Hi,

I asked customer of an IEC 62040-3 example report which he has from other manufacturers.

He sent the attached pdf which has a technical specification of a UPS in accordance with IEC/EN 62040-3. He mentioned this is only a sample file which has been downloaded from Internet and some of its internal data (e.g. subclauses' numbers and specifications) are not correct, however it can be considered as a reference. He explained further that the parameters mentioned in the tables should be declared by manufacturers prior of sample testing procedure.

Hope the attached helps in finding the test report for SURT1000XLI asap.

Thanks
Saeed

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

where was it indicated that this report was available? i havent seen where such a report exists but if you can let me know, i'll look into it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

Sorry, something is missing from my above reply, so sending again:

Thank you for kindly trying to help.

In APC Smart-UPS RT brochure attached, 2nd page on left hand side (in blue, regarding SURT features), right at the bottom of page includes below point:

Warranty & Approvals:

Performance: IEC 62040-3, EN50091-3

Now for a banking ATMs project because APC SURT1000XLI is included in our proposal, for comparison reasons we are asked to provide:

Test report for " IEC 62040-3 Performance Approval for APC Smart-UPS RT 1 kVA"

All other approvals are given in APC web apart from this one.

Is there a general report for the mentioned performance approval in the catalogue? Or should customer mention the desired tests which they require the report for?

Kind regards
Saeed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

i am trying to track this down for you. i'll post back when i have some info.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:48 AM

Thanks very much again for kindly trying to help us.

Just a point to mention, according to a communication which we did with regards to specifying comparison items, they mentioned below required sections (or certain tests) of the report:

6.3.4.1, 6.3.4.3, 6.3.5.1, 6.3.5.2, 6.3.6.1, 6.3.6.2, 6.3.6.3, 6.3.7.1, 6.3.9.1, 6.3.9.2, 6.6.5, 6.6.2.6

I searched web and found the attached document " International Standard IEC 62040-3 {ed1.0}en ". The doc indicates for example:

6 Electrical tests for UPS
6.3.5 UPS output characteristics – Overload and short-circuit

Looking at this doc it seems customer has certain test values (numbered items above) and intends to compare them with the unit's test report or one can conclude that the standard can be describing test methods i.e. this is a standard (62040-3) to control if the tests of the ups device are made according to the known standards, (for example: at the non-linear load).

Honestly speaking, after studying it is not yet clear the scope and object of the standard.

Please can you help.

Kind regards
Saeed

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:47 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:47 AM

i found some information..the IEC 62040-3 performance approval is not really a test report. it is a standard that companies use to verify that their product meets a certain criteria from the standard.

in regards to those standards that you mentioned, i will see what we have for them.

thanks though, what you mentioned is helpful so that i can see what data we have.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:47 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:26 AM . Last Modified: ‎2024-03-14 12:47 AM

Thanks very much for trying to help me.
I was confused a bit, now is making sense after your answer and kind pursuits of an APC engineer in our region, thanks a lot, but unfortunately he couldn't go further with details of the specified tests.
Pls help me with any docs you may have. It will be great to show in this project that APC is the best choice by far for their requirement.
Kind regards
Saeed

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

0 Likes
0
2630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

Thank you very much for the documents, they are good and should be helpful.

Almost all the standards and approvals which are listed by APC for SURTs are available in APC web and are already given to customer but they are specificly asking for the numbered sections mentioned above from performance approval IEC 62040-3 for SURT1000XLI.

We have discussed with them the purpose of the IEC 62040-3 but still they insist in having the required certain test reports as shown above.

If possible pls help me with any of the one of the reports that they are asking. If not available pls can you guide me about what our final words should be to customer about his requested items.

Sorry, seems the subject in discussion is a difficult one but lets see if anything exists about their specific request.

Thanks
Saeed

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

0 Likes
0
2631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:27 AM . Last Modified: ‎2024-03-14 12:47 AM

Hi,

I asked customer of an IEC 62040-3 example report which he has from other manufacturers.

He sent the attached pdf which has a technical specification of a UPS in accordance with IEC/EN 62040-3. He mentioned this is only a sample file which has been downloaded from Internet and some of its internal data (e.g. subclauses' numbers and specifications) are not correct, however it can be considered as a reference. He explained further that the parameters mentioned in the tables should be declared by manufacturers prior of sample testing procedure.

Hope the attached helps in finding the test report for SURT1000XLI asap.

Thanks
Saeed

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of