Symmetra stuck at "Please Wait"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra stuck at "Please Wait"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
6
1717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

Symmetra stuck at "Please Wait"

I have a Symmetra which has been running great for 10 years. We had an extended power outage yesterday, and when power came back on the symmetra is stuck at "Please Wait..." (10 hours later)

I've tried cycling power to unit, etc. No difference. I'm in bypass mode now but need to get this online.

When I access the web management card in the unit I see "Searching for a Symmetra Power Array..."

Can anyone suggest diagnostic steps - or point me in the right direction? (The web management card is the only add-on card in the unit).

I have 2 management modules on the top shelf (main and backup), 2 battery packs, 1 power module, and the built-in stuff on the lowest shelf...

Thanks!

---------------------
In case it matters, here is some info on the web management card:

Model Number: AP9606
Serial Number: WA0010011173
Hardware Revision: G9
Manufacture Date: 03/06/2000
MAC Address: 00 C0 B7 63 C2 A7
_
Application module information
Name: sy326a.bin
Version: v3.2.6.a
Date: 07/31/2002
Time: 12:36:59
_
APC OS(AOS) information
Name: aos326b.bin
Version: v3.2.6.b
Date: 09/16/2003
Time: 07:45:28

Message was edited by: ocgltd

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • please
  • symmetra
  • ups
  • wait
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

yes, I am an APC employee. you're welcome.

not sure who you were speaking to but I was able to add it to the cart on the APC website?

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SYMIM2

we still sell it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

hi michelle,

the powerview and network card are telling us it cant talk to the UPS. this generally tells us there is an issue with the intelligence modules. if you need immediate support, i'd recommend contacting APC at 800-890-4272 to get you back up and running quickly.

if you are ok with forum support, please tell us what LEDs you see on your main intelligence module, from left to right. the main intelligence module is the bottom intelligence module on the top right level of the system. the redundant is on the top. please tell us what LEDs you see on there from left to right as well.

lastly, what position is the maintenance bypass breaker in? this is located on the bottom level of the system and is labeled - it can be either "up" or "down."

thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

Thanks for the reply! I would like to try to take this as far as I can...so here's what I've done:

ALL LEDs were off on BOTH MIM & RIM

I removed the MIM and the RIM immediately came to life (I heard clunking of a big relay as I did that)

With the MIM removed, the RIM shows three LEDS: ORANGE+GREEN+GREEN.

The display warned my that:
1. the unit is in bypass (correct - I switched it to bypass to restore power to the servers)
2. the MIM was removed (correct - I pulled it)
3. That "Redundant Intellig. Module is installed and failed"

Dam...does that mean the MIM and RIM both failed at once?! Seems unlikely...just 24 hours ago the system showed everything operating normally!

The big questions:
1. What do the 3 LED's mean (left to right)?
2. The display shows RIM in ctrl, but load and bat capacity are blank. Does that mean that the unit cannot resume operation (RIM failed too?)
3. It seems unlikely that RIM + MIM both failed at once?! If there a way to reset them?

Other ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

And a little more info:
The MIM p/n is 885-6622D/8
The RIM p/n is 885-6623D/8

I found some SYMIM2 and SYRIM2 for sale online - (not sure I'm ready to buy yet but just in case)...do the p/n have to match or will any SYMIM2/SYMRIM2 work?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

Ok, on the SYMIM2: there should be (4) LEDs total, left to right - Red - MIM fault, Yellow/amber - System Fault, Green - in bypass, Green - Load powered. For the RIM, you will also see four LEDs, left to right: Red - RIM fault, Yellow/amber - RIM in control, Green - in bypass, Green - Load powered.

On this system, the RIM only encompasses 30% of the functionality of the MIM. the idea is for it to kind of hold your current status of the system of the MIM if it fails. Thus, to get the system properly working again, you may need a new MIM. the RIM cannot take the UPS out of manual bypass even if you flip the switch to do so. it does not have the capability.

if it were me, here is what I would do:

1.) remove both SYMIM2 and SYRIM2 (which those are the only part #s we go by at APC) from the system.
2.) since you are in bypass, let's just start with the SYMIM2. remove the RIM and insert the MIM only and tell me what you get for LEDs and on the screen with just the main intelligence module in.

if i had to guess, it sounds like a bad main module but keep in mind its 10 years old, so it may not be a bad idea to just get one SYRIM2 and one SYMIM2 on order. who knows - during the outage, maybe the batteries heated up a little bit and aggravated those modules. hard to say.

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

Nothing happens even if the MIM is in alone, so looks like a malfunctioning MIM. So I've started the process of buying a replacement.

I'm not sure if you're an APC employee but I appreciate the online help.

My experience with APC has been so good that I decided to buy the new MIM from APC. Sadly I spent 20 minutes on the phone with an APC sales & support person who told me that APC does not sell this part.

Strangely newegg and others do offer it so I'll go that way...

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

0 Likes
0
1717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:04 AM

yes, I am an APC employee. you're welcome.

not sure who you were speaking to but I was able to add it to the cart on the APC website?

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SYMIM2

we still sell it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore