Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
I have a Symmetra LX 160000 that I would like to increase the batteries on. Currently has two batteries and two power modules. If I want to add a third battery do I need do add another power module? Do power modules and batteries need to "pair" up?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
No, they don't. You can scale both power modules and batteries for power and batteries as you see fit - which is one of the major benefits of the system. You could have one power module with four batteries for example.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:48 AM
No, they don't. You can scale both power modules and batteries for power and batteries as you see fit - which is one of the major benefits of the system. You could have one power module with four batteries for example.