Is there any way to cause an AP9631 equipped UPS to signal its clients that the UPS is shutting down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is there any way to cause an AP9631 equipped UPS to signal its clients that the UPS is shutting down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
9
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Is there any way to cause an AP9631 equipped UPS to signal its clients that the UPS is shutting down

Hi everyone,

Is there any way to cause an AP9631 equipped UPS to signal its clients that the UPS is shutting down without actually shutting down – this is obviously for testing purposes. I want to signal the clients that the UPS is going down and observe the behavior of the clients.

I do NOT want to physically cause the UPS to cut power however. I see where the function is but it looks like it will shut down the UPS in actuality and that is what I do NOT want to happen:

Thank you!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9631
  • emulate
  • initiate
  • shutdown
  • signal
  • simulate
  • test
  • virtual
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Hi Boyan,

You can always use our TestDrive Link for live simulation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Hi Boyan, 

The only work around I can think of to avoid having the UPS actually shut down would be to configure the PowerChute Network Shutdown clients to shut down when the UPS is on battery. Then you would be able to pull the plug on the UPS, effectively putting it onto battery and causing PowerChute to initiate a shutdown. Then you can plug the UPS back into utility without it having to shut down at all. 

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Thanks Nicole,

That might work; on another subject is there such a thing as AP9631 software emulator? Say an OVA which emulates an AP9631 and one can control completely outside the physical world? That would ease testing quite a bit when building new infrastructure...

Thanks

~B

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Another approach I've heard of is to configure PCNS to shutdown on over-temperature. Then change the temperature threshold to trigger the shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

@voidstar that's a great idea. Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Hi Boyan,

You can always use our TestDrive Link for live simulation.

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

@Jonathan Thank you so much; I did not think that such solution would exist! Good work for making this available. I will point my PCNS to the simulated card and do it that way. Cool!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

You are very much welcome, keep us posted!

Reply

Link copied. Please paste this link to share this article on your social media post.

bbiandov_apc
Lieutenant JG bbiandov_apc
Lieutenant JG

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

Hi Jonathan, I tired it out but I get time out error; could this be due to NAT? Obviously I am coming from a private IP which is xlated onto public and that's how your emulator sees me?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
2497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

Hi,

You cannot connect to the simulated UPS / NMC. Your best option is what VoidStar wrote. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore