Help on calibrating Smart-UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Help on calibrating Smart-UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
1
3093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

Help on calibrating Smart-UPS

Hi

I need guidance on calibrating UPS. I have onsite three types of UPS

Smart UPs 750

Smart-UPS 3000

Symmetra LX 16000

I want to calibrate all 3 and do this from the Network card/Web interface. My question is this. I can see from other discussions mention of a 30% load. However I think this might apply to doing the calibration manually and on older UPS. Do I need to have a 30%+ load on these types when doing it via the webpage. If so why and where is the APC guidance on this (as I have yet to find it).

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
3092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

For any UPS, there are certain conditions that need to be met in order for the UPS to accept a command to run a runtime calibration to ensure the calibration is as accurate as possible and worthwhile. Make sure you only do a runtime calibration 1-2 times a year or after you replace the batteries.

In general, you can find some of this information in the knowledge base and within the product user's guides.

  1. The UPS must be online and report 100% charged. Specifically the symmetra LX, typically you will see 99% where the UPS does not report 100% because conditions are not suitable (constant load fluctuations, modules have been been inserted/removed, etc). You'll need to wait until it shows 100% on any UPS though which can be maybe later at night after load fluctuations calm down.
  2. In a manual calibration we do suggest 30% load and it cannot fluctuate +/- 5% to ensure accuracy of runtime. I would say the minimum is 20% load and any lower will be a waste of time. I'd go with 30% and make sure it does not fluctuate more than the +/- 5% to ensure accuracy if you can. Certain model Smart UPS will also refuse the calibration if the load is below 10% but again, the lower the load, the less accurate the results.
  3. If you do a manual calibration, you won't need to wait for the UPS to say 100% vs. 99% but you'll need to sit and watch the UPS and make sure you reapply AC power to it when its complete. The software command will discharge the UPS down to 10-20% and charge itself back up with out you sitting there. If you choose manual calibration, you should remove any data cables and management cards during this process and let your UPS discharge until it turns off then re-connect it to AC power. This is not preferred when you can just meet the criteria in #1 and #2 and just use the command via management card/software.
  4. Keep in mind that any time the UPS goes to battery during long power outage (when it gets discharged to around the same 20% battery capacity), it is ultimately calibrating itself at that point too. Runtime accuracy is updated when the UPS goes on battery at any point while when it is online, it is a really good estimate.

Hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
3093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

For any UPS, there are certain conditions that need to be met in order for the UPS to accept a command to run a runtime calibration to ensure the calibration is as accurate as possible and worthwhile. Make sure you only do a runtime calibration 1-2 times a year or after you replace the batteries.

In general, you can find some of this information in the knowledge base and within the product user's guides.

  1. The UPS must be online and report 100% charged. Specifically the symmetra LX, typically you will see 99% where the UPS does not report 100% because conditions are not suitable (constant load fluctuations, modules have been been inserted/removed, etc). You'll need to wait until it shows 100% on any UPS though which can be maybe later at night after load fluctuations calm down.
  2. In a manual calibration we do suggest 30% load and it cannot fluctuate +/- 5% to ensure accuracy of runtime. I would say the minimum is 20% load and any lower will be a waste of time. I'd go with 30% and make sure it does not fluctuate more than the +/- 5% to ensure accuracy if you can. Certain model Smart UPS will also refuse the calibration if the load is below 10% but again, the lower the load, the less accurate the results.
  3. If you do a manual calibration, you won't need to wait for the UPS to say 100% vs. 99% but you'll need to sit and watch the UPS and make sure you reapply AC power to it when its complete. The software command will discharge the UPS down to 10-20% and charge itself back up with out you sitting there. If you choose manual calibration, you should remove any data cables and management cards during this process and let your UPS discharge until it turns off then re-connect it to AC power. This is not preferred when you can just meet the criteria in #1 and #2 and just use the command via management card/software.
  4. Keep in mind that any time the UPS goes to battery during long power outage (when it gets discharged to around the same 20% battery capacity), it is ultimately calibrating itself at that point too. Runtime accuracy is updated when the UPS goes on battery at any point while when it is online, it is a really good estimate.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.