Smart-UPS 3000 RM XL - runtime question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 RM XL - runtime question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
6
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Smart-UPS 3000 RM XL - runtime question

HI ,

I have a Smart-UPS 3000 RM XL , (SUA3000RMXLI3U).


Last week I got the red battery light appear , so I have just put in a new battery and have performed the self test , the red light has now gone and the test passed.


Currently it is saying the the load in watts is 50.7% with a battery capacity of 100% and is showing a runtime of just 6 minutes.


The runtime seems very low , should I expect more than that with this model with a new battery?


Thanks.

Scott





Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

This should answer your questions -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Your runtime is reported as 1 minute so that is likely the root of the problem. You can issue a calibration via the UPS Network Management Card you seem to be using via the diagnostics menu but alternatively, you can also do a manual runtime calibration, if that fails, as outlined in the article.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

HI ,

I have a Smart-UPS 3000 RM XL , (SUA3000RMXLI3U).


Last week I got the red battery light appear , so I have just put in a new battery and have performed the self test , the red light has now gone and the test passed.


Currently it is saying the the load in watts is 50.7% with a battery capacity of 100% and is showing a runtime of just 6 minutes.


The runtime seems very low , should I expect more than that with this model with a new battery?


Thanks.

Scott





Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Ok , I will give it 24 hours with the new battery before running it. thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Great thanks , that sounds straightforward.

Would it be ok to run this during production hours?, or should my servers and other devices be shut down first?

thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:49 AM

Up to you - if you have an outage during the day during this time period, then the UPS might be discharged from running the calibration and not provide enough battery back up time. If you're not expecting any issues, there would be no problem running it during the day technically as the UPS will discharge itself down to 10-20% capacity and charge back up. No need to turn the servers off in my opinion.

Now, if this was not a brand new battery, then i'd tell you to make a judgement call as older batteries that may need replacing soon could fail during a deep discharge and cause unexpected results or extremely low runtime. This is definitely not typical though and it doesn't really make sense to me to do a runtime calibration on batteries older than 3-5 years that are constantly being used during power outages.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

Hello,

have a similar problem, the battery is new and installed 5 months ago, but i don't know how long ago the alert "battery discharged" appeared. There is UPS status:

Last Battery Transfer:Due to software command or UPS's test control
Internal Temperature:17.5°C
Runtime Remaining:1 minute

Power

Input Voltage:226.0 VAC
Output Voltage:226.0 VAC
Frequency:50.0 Hz

Load

Load Power:22.7 %Watts
Apparent Load Power:23.4 %VA
Load Current:2.6 Amps

Battery

Capacity:100.0 %
Battery Voltage:54.54 VDC
External Batteries:0

UPS model is sua3000rmxli

what can be done in this case? if runtime calibration is useful in this case, how to do this calibration for this model?

thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:49 AM

This should answer your questions -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Your runtime is reported as 1 minute so that is likely the root of the problem. You can issue a calibration via the UPS Network Management Card you seem to be using via the diagnostics menu but alternatively, you can also do a manual runtime calibration, if that fails, as outlined in the article.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of