Symmetra PX 80kw showing zero input frequency

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 80kw showing zero input frequency
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
3
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

Symmetra PX 80kw showing zero input frequency

Hello,

I am hoping someone might have seen this issue / has an idea where to start looking for a fix.  I have a APC Symmetra PX 80KW that I am setting up and everything seems fine but when turning on the ups I  get "AC adequate for UPS but not for bypass"  the ups starts and seems fine,  runs on bats, etc.   I did scan through the menu and see why its giving that message,  it shows "Input Frequency 0 hz .   

Has anyone had this problem before?   where does the UPS read the frequency from?   The 480v to 208/120 MBP shows the correct 60hz

Thanks for any help. 

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

Problem solved,  just in case someone searches for it again. 

I scanned over another PX80 that we have,  it seems this unit must have had a external bypass setup,  it was missing the bus bars between Mains input and bypass.   once installed the unit was fine.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

I'm not very familiar with the UPS -- I've worked mostly with the modular distribution panel. The message indicates while the UPS can run on the incoming AC, it's not acceptable to feed directly to the load (ie, bypass). If the input frequency shows 0Hz, maybe the phase rotation is wrong? You can call APC to get in contact with support specialists who are familiar with the Symmetra PX 80kVA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

Thank you for the reply,  I checked the phase rotation today and it is good,  Clockwise.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:25 AM . Last Modified: ‎2024-03-19 02:22 AM

Problem solved,  just in case someone searches for it again. 

I scanned over another PX80 that we have,  it seems this unit must have had a external bypass setup,  it was missing the bus bars between Mains input and bypass.   once installed the unit was fine.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore