Symmetra LX Swollen Batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX Swollen Batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
5
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

Symmetra LX Swollen Batteries

We have a Symmetra LX unit that has 2 swollen (and dead) battery modules in it. We are unable to remove the 2 batteries from the chassis. I've turned the batteries off and let them sit for a couple of days and we are still unable to remove them.

We had an older Symmetra 16000 unit that also had swollen batteries that we couldn't remove. We ended up loosening the large bolt at the top of the unit and were able to lossen each individual shelf enough to loosen the batteries and remove them.

Since the LX unit looks like a solid steel enclosure all the way around, I don't see any way to do the same trick on the LX unit. Anyone have any other suggestions on how to get the batteries out? This unit is not covered under warranty any more.

--greg

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

So the SYBT5 modules were not swollen, and it was just an issue of clearance to get the module unlocked from the bay. Sometimes there is just barely 1-2mm clearance between the top of the SYBT5 and the sheet metal of the chassis bay above it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

Are you certain they are swollen? How long was the Symmetra LX complaining of the bad battery modules? Do you know that serial numbers of each SYBT5?

It is sometimes necessary to briskly pull up on the battery module handle to get the battery unlocked from the bay. I would imagine that if the battery was truly swollen, you would be able to begin removing the battery module but it would then get "wedged" into place.

Your best option is to call into our phone support 800-800-4272 to ensure that everything else with your Symmetra LX is in proper working order, including the environment in which it is installed and the methods it can use to notify the customer of issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

Of course, if they are swollen, the plain and simple fact is that they will have to be replaced. I've even had afew where the batteries swelled enough, that getting out took over 3 hours of coaxing, and moving them half a millimeter at a time. Circle in a square hole of course.

Find out your RBC battery type for replacements. If you have no warranty on your unit, you don't necessarily need to purchase batteries from APC. You will need to know the AMP and voltage of the battery(s) in question for the correct replacement. Be sure to keep all CONNECTORS, and if any, fuses, that are on the battery(s) you have in need of replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

The point JoeMomma is trying to make here, as he and I have discussed in the past, is that there have been no instances of swollen SYBT5's, so he's trying to collect more information about it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

The unit has SYBT5 modules in it. We were finally able to get them out of the unit. We ended up having to shove a screwdriver under each module to lift up and then pull the battery out. Just pulling up on the battery module itself wasn't enough to get it over the lip on the chassis.

And we also determined that this unit is still covered under warranty despite what APC told us at first. New modules are on the way!

--greg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

0 Likes
0
934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:04 AM

So the SYBT5 modules were not swollen, and it was just an issue of clearance to get the module unlocked from the bay. Sometimes there is just barely 1-2mm clearance between the top of the SYBT5 and the sheet metal of the chassis bay above it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore