Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Matrix 3000 & 5000 Wiring Inquery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 3000 & 5000 Wiring Inquery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
3
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

Matrix 3000 & 5000 Wiring Inquery

Hello all! First time poster, here.

In amidst my APC collection lay a Matrix 3000 (MX3000EU / WM0051012276) and a 5000 (MX5000PE / EM9832002476). Both currently untested, by being plugged in (which is the issue), and powered from the installation of batteries.

The 3000 I found in Seattle at a place called RE-PC (http://www.repc.com) and sold "as is". It came with one Smartcell XR battery unit (4 batteries to hold) with NO batteries in it. The cord of the 3000 unit, seems to have had bolt cutters or something taken to it, as it is now has a (perhaps) 6in from the base "stub". That's not a real issue as I'm certain I can still place the correct plug type on it despite it being as short as it is, and create a longer extension cord later on to hook into it.

Since I've tried and failed to find specs on these devices, both on the APC site and Google / Altavista, my questions are these:

1) Are these units 30a / 208v or 30a / 240v?
2) I suspect 208v but would they suffer damage if connected to a 30a / 240v socket for power?
3) In a twist lock 30a / 240v, are there TWO hots and a ground? Or the usual hot / neutral / ground?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

I would be weary of buying "as-is" units that have been long discontinued at APC. If you find that there are issues with the Electronics Unit or Isolation Unit (top and bottom sections of the Matrix-UPS, respectively), there will be no easy way to obtain replacement parts.

You can view the tech specs and documentation for the [5000VA|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=mx5000] and [3000VA|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=mx3000] Matrix-UPS on our website.

To answer your specific questions:

1) Both varieties of Matrix-UPS is designed for either 208v or 240v (hot-hot-ground) 30 Amp service typically supplied by a L6-30 NEMA outlet.
2) Matrix-UPS does not prefer either 208 or 240vAC. It has a fairly liberal input voltage range for normal operations: 156 - 252v (208v) / 176 - 282v ( 240V)
3) NEMA L6-30 is always hot-hot-ground. It is assumed that any L6-30 outlet has been properly installed by a licensed electrician and supplied by at least a 30A upstream breaker.

The Matrix-UPS can output any combination of 120v, 208v, or 240v any time by way of its built-in isolation transformer.

You need to purchase a single RBC14 to fill that SmartCell XR cabinet with the 4 batteries (RBC14 is a kit including all 4 separate batteries).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:47 AM . Last Modified: ‎2024-03-08 04:05 AM

I would be weary of buying "as-is" units that have been long discontinued at APC. If you find that there are issues with the Electronics Unit or Isolation Unit (top and bottom sections of the Matrix-UPS, respectively), there will be no easy way to obtain replacement parts.

You can view the tech specs and documentation for the [5000VA|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=mx5000] and [3000VA|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=mx3000] Matrix-UPS on our website.

To answer your specific questions:

1) Both varieties of Matrix-UPS is designed for either 208v or 240v (hot-hot-ground) 30 Amp service typically supplied by a L6-30 NEMA outlet.
2) Matrix-UPS does not prefer either 208 or 240vAC. It has a fairly liberal input voltage range for normal operations: 156 - 252v (208v) / 176 - 282v ( 240V)
3) NEMA L6-30 is always hot-hot-ground. It is assumed that any L6-30 outlet has been properly installed by a licensed electrician and supplied by at least a 30A upstream breaker.

The Matrix-UPS can output any combination of 120v, 208v, or 240v any time by way of its built-in isolation transformer.

You need to purchase a single RBC14 to fill that SmartCell XR cabinet with the 4 batteries (RBC14 is a kit including all 4 separate batteries).

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

The input on the Matrix line of UPS systems would be 30a, 208 or 240 single-phase. The default is 208v; for 240v use you must change the input voltage selector on the UPS. The unit uses an L6-30 connection for an input cord.

The Matrix would not suffer damage when used with a 30a 240v connection assuming the wiring was done properly.

For the input on the unit, 240v would require H H G wiring scheme, as would a 208v wiring input.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

0 Likes
0
826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:48 AM . Last Modified: ‎2024-03-08 04:05 AM

I take it that the (HOT) wires are both 120-125v each, thus create the 240v?

Though I know the RBC14 cells are available through APC, I have a local place where I can aquire the required 70amp 12v replacements.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore