Symmetra LX Load Balancing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX Load Balancing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
2
1223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Symmetra LX Load Balancing

I currently have a Symmetra LX 16KVA system that is powering a breaker box. The breaker box is currently powering 10 wall outlets, which in turn have the PDUs in our two racks snaked across the floor to. We want to find a better solution that involves rewiring the breakers to outlets above the server racks and a two post demarc. Does anyone have any suggestions for how to balance this power distribution to TrippLite PDUs (15 outlet, 15 amp) above the racks? Or does anyone know a good certified electrician that has experience in these matters in the Pittsburgh area? I'm open to either of these options.

FYI
Assume two racks full of servers that all have dual power supplies so splitting the legs would probably be a good option to.

AND the breakers in the box are only 20a.

Message was edited by: joshrock11

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • electrician
  • load_balance
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

It sounds like you will powering mostly 120vAC equipment. If this is the case, splitting the legs on the output of the UPS will be the best solution for you. The legs should already be split to the panel (4 wire output from the UPS), so reconfiguring an equal number of breakers on each leg will be the next step. A quick prewire calculation of the pieces of load in each rack will help you ensure the 2 legs end up having about the same load on them. Once your rewiring is complete, as you power your load up, you will be able to see immediately the draw on each leg, through the status menu of the display panel. This can be a final step to making sure your load ends up being about even on both legs.

Good luck!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

Hello,

For your electrician needs request I would recommend that you contact our Man Rep. in your region. Here are his contact details:

Renaissance Electrical
Phil Hollern (phil@renmarkusa.com)
(p) 724.935.6682


For your load balance question someone else from the community should respond shortly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

0 Likes
0
1224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:45 AM . Last Modified: ‎2024-03-08 02:00 AM

It sounds like you will powering mostly 120vAC equipment. If this is the case, splitting the legs on the output of the UPS will be the best solution for you. The legs should already be split to the panel (4 wire output from the UPS), so reconfiguring an equal number of breakers on each leg will be the next step. A quick prewire calculation of the pieces of load in each rack will help you ensure the 2 legs end up having about the same load on them. Once your rewiring is complete, as you power your load up, you will be able to see immediately the draw on each leg, through the status menu of the display panel. This can be a final step to making sure your load ends up being about even on both legs.

Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore