Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Symmetra 80K THORC456 shows a few messages in the event log like this :
05/20/2015 17:16:32 UPS: Power Module failure cleared.
05/20/2015 17:16:12 UPS: Power Module failure.
05/20/2015 17:16:04 UPS: Power Module failure cleared.
05/20/2015 17:15:44 UPS: Power Module failure.
05/20/2015 17:15:43 UPS: Power Module failure cleared.
05/20/2015 17:15:23 UPS: Power Module failure.
Physically all the module are normal and operation . please let me the what could be root cause for the above events
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Hi,
I think input mains was out of telerance for short time (about 20 seconds)
Regards
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Kindly guide me , am waiting
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Hello,
This support platform is not intended for urgent issues. If you require urgent support, please contact your local technical support office here -> http://www.apc.com/site/support/index.cfm/contact-information/
Regardless, we can't do much about that type of issue here anyway. One or more modules likely have a fault condition that comes and goes. You'll want to contact your local technical support office and they'll ask you for special log files they can hopefully decode and understand what the fault is. Then, if you're under a service contract, send appropriate parts or field service technicians to your facility.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 01:21 AM . Last Modified: 2024-03-19 02:26 AM
Hi,
I think input mains was out of telerance for short time (about 20 seconds)
Regards
Link copied. Please paste this link to share this article on your social media post.