Symmetra 16 KVA doesnt recognize XR battery frame

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra 16 KVA doesnt recognize XR battery frame
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
5
1332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Symmetra 16 KVA doesnt recognize XR battery frame

Our Symmetra 16KVA has an XR frame with 12 SYBATT modules but now it only reports the main frame's batteries.

We pulled out old batteries and inserted newer ones, leaved only new ones and it was the same situation.

Before this it was reporting randomly NUMBER OF BATTERIES decreased/increased messages.

We were thinking that maybe the problem is in the SYCC communication Card. Is this card Hot Swappable?

Can we change it without turning off the UPS?

We will appreciate any help

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Hello

  1. Can you clarify - on the XR frame, is the display lit up? If so, what do you see on it?
  2. Have you verified the "phone cable" looking connection going from Symmetra Comm Card on the UPS (yes its hot swappable) and the connection on the rear of the XR frame?
  3. Can you measure the DC voltage on the anderson connector on the XR frame?
  4. In the status menu on the powerview on the UPS, what is the actual battery voltage reported as?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Hello

  1. Can you clarify - on the XR frame, is the display lit up? If so, what do you see on it?
  2. Have you verified the "phone cable" looking connection going from Symmetra Comm Card on the UPS (yes its hot swappable) and the connection on the rear of the XR frame?
  3. Can you measure the DC voltage on the anderson connector on the XR frame?
  4. In the status menu on the powerview on the UPS, what is the actual battery voltage reported as?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Hello Angela, First of all thank you a lot for your answer, it has been very helpful, in fact with your advise we have already fix the problem.

1. The XR frame display was off.

For some reason the anderson connector was loose, maybe the air cooling  mainteinance men moved the frame.

At first it was only a false contact and we got erratic messages like bad batteries, high temp. on them etc.

2. We have  had already tested the "phone cable" in another working Symmetra.

Are 885-6625/1 and 885-6625/5 Comm Cards interchangeable? we got a spare one of the first.

3.is No need now. is it?

4.In the status menu it is displayed:

    Bat. voltage: 130.6 volts

   Bat. Cappacity :100%

   Run Time: 1Hr. 56 min

    !4 Batts, 0 Bad

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

It sounds like you just have different revisions of the phone cable. As long as they have the same main part number, should be the same cable.

I would just keep an eye on the battery voltage. It says 130.6V now and ultimately should get to 136-138V. Check it in 24 hours to ensure it has climbed now that the XR frame is charging.

Glad you got it working.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Yes, any communication cards on this UPS and the XR Frames are hot swappable. The only thing you'll loose is temporary monitoring of the respective device in some sense.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

0 Likes
0
1331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:19 AM . Last Modified: ‎2024-03-12 11:44 PM

Hi Angela,

Our Syymmetra continues working fine.

The  battery voltage was bellow 136V because  a bad battery module, today it reported high temperature we taked it out and now we have 136.7 volts reported on the powerview status menu. 

The part numbers I told you before arent phone cables but Communication Card ones, those are what we need to know if are hot swappable and also if we can interchange them.

Thank you again,

Jose

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore