Symettra LX XR Frame errors

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symettra LX XR Frame errors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
8
4283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Symettra LX XR Frame errors

We have an XR Frame giving errors E7 and EA.  At first the main unit was reporting errors however the XR frame display was only displaying its number (02).  I have completely disconnected the unit to power down and bring it back up, no luck.

I've racked the main card and inspected, nothing obvious.  I've found information here on the E7 fault but cannot find anything on EA fault.  Shame on APC for not even putting a user manual on the website, just a quick-start guide which is useless for problems like this.  Data from the unit is

I2cExternalBusFault E_7

RemoteOnCircuitFault E_A

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

I would probably focus on the E7 first which is a communication issue - which I know you might have found some information on. Solving the E7 could also solve the EA.

Do you have more than one frame - if so, is E7 only on this one? Do you have another spare Symmetra XR Communication Card to see if the issue follows the card and swap them? This could also be an issue with the communication card on the UPS or the XR frame itself - you could try reseating both to power cycle them and verify they are properly secured and installed.

The next thing that could cause this is a problem with the communication cable between the XR frame and the UPS or XR frame to XR frame.

And less commonly, (because you'll likely see other symptoms), a main intelligence module problem because many other things would not work.

How long was the frame working properly for? Just briefly or for months or years?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

We have an XR Frame giving errors E7 and EA.  At first the main unit was reporting errors however the XR frame display was only displaying its number (02).  I have completely disconnected the unit to power down and bring it back up, no luck.

I've racked the main card and inspected, nothing obvious.  I've found information here on the E7 fault but cannot find anything on EA fault.  Shame on APC for not even putting a user manual on the website, just a quick-start guide which is useless for problems like this.  Data from the unit is

I2cExternalBusFault E_7

RemoteOnCircuitFault E_A

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

I would probably focus on the E7 first which is a communication issue - which I know you might have found some information on. Solving the E7 could also solve the EA.

Do you have more than one frame - if so, is E7 only on this one? Do you have another spare Symmetra XR Communication Card to see if the issue follows the card and swap them? This could also be an issue with the communication card on the UPS or the XR frame itself - you could try reseating both to power cycle them and verify they are properly secured and installed.

The next thing that could cause this is a problem with the communication cable between the XR frame and the UPS or XR frame to XR frame.

And less commonly, (because you'll likely see other symptoms), a main intelligence module problem because many other things would not work.

How long was the frame working properly for? Just briefly or for months or years?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Single UPS, Single XR, Single Cable so no opportunity to swap things around to see if the fault moves.  Unit is 13th week of 2010 manufacturer and I believe went in in late 2010 and the problem has only now developed.

All cables are properly installed and secure.  Shutting the UPS down is not an option without considerable notice.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Hello,

Thanks for the information. To clarify, I did not suggest power cycling the UPS or anything that would affect the UPS output. You can start by just power cycling the communication card on both the UPS and the XR frame which do not affect UPS power output.

If you have access to the pre-installed Network Management Card, the event.txt may also help verify no other problems exist. (Instructions here on downloading event.txt -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Hello,

The UPS communication card SYAFSU15 (where the XR communication cable connects to and has the DB-9 serial port).

The XR communication card that goes in the battery frame itself is SYAFSU16.

The communication cable that looks like a phone cable is 0W6002B.

If I had to guess, more often than not if there are no other communication problems in general, it is likely the SYAFSU16 in the XR frame. Or at least what we'd try first.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Hi Angela,

Can you advise part numbers for the communication card and cable?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

Thanks Angela,

This information is extremely difficult if not impossible to find and I'd like to say that we shouldn't need to rely on a forum to obtain the part numbers.  I spoke with the technical assistance line and they could not give me the ...15 number you have provided.  There is no user manual available with information on error codes just a basic information sheet on installing the system.  I have requested pricing and availability from our local distributor for these parts and will advise if we have been successful in resolving this issue, if for no other reason than to assist other APC customers.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
4278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

No problem.

I am not sure why the part numbers are not listed. I cannot vouch for support worldwide but I know NAM support would've been able to provide those part numbers without a doubt. If you wanted to pass along a case number or reference number, I could see if I could have someone in your region look at what happened here as to why part numbers were not available to tech support. Worldwide tech support has access as to where to find them, just as I can look them up.

I found some information on the website too as far as accessories but it was a little difficult to find: http://www.apc.com/template/size/apc/sizing_display_options.cfm?option_type=SparePart&ups_sku=SYA16K... It also does not include the communications cable since it is a "part" versus SKU.

I am thinking I might ask at least for a knowledge base to list all available part numbers (if it is possible) which will be quicker than any adjustments to the user's guide.

*Edit* - Someone did show me http://www.apcmedia.com/salestools/SCON-8SRKKA/SCON-8SRKKA_R1_EN.pdf which is available on the documentation tab of each product SKU on apc.com. But, this is a NAM based document. http://www.apcmedia.com/salestools/SCON-8SBNC7/SCON-8SBNC7_R1_EN.pdf is the international one because I have a feeling you are not based in NAM. Starting on page 41 in both documents, we have lots of spare parts listed but I still think having it in multiple places will be a good idea. The part numbers I gave you though apply to all units. Only certain things, usually power related, are different for the NAM or International units.

*EDIT #2* - I am on a roll here and will scold myself shortly yell. Let's confirm the frame SKU and XR battery cabinet model you have. I forgot the LX can use two different models of frames (a "Symmetra LX" battery frame and also an older "Symmetra" frame that uses SYBT2 batteries and I of course want to make sure I got you the right parts. I made a few assumptions and shouldn't have.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore