UPS Error Regarding automatic voltage regulator (AVR)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS Error Regarding automatic voltage regulator (AVR)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
6
3597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:17 AM

UPS Error Regarding automatic voltage regulator (AVR)

I had this set of errors come across the other day and I am trying to determine what needs to be done as far as hardware goes.

04/03/201410:08:42UPS: An automatic voltage regulator (AVR) relay fault no longer exists.0x0127
04/03/201410:08:42UPS: Started a self-test.0x0137

Restarted the UPS.

04/02/201412:50:57UPS: The output power is turned off.0x0114
04/02/201412:50:55UPS: No longer in bypass.0x011E
04/01/201414:31:01UPS: Refused a self-test; UPS is overloaded.0x0106
04/01/201414:30:54UPS: An automatic voltage regulator (AVR) relay fault exists.0x0126
04/01/201414:30:53UPS: In bypass in response to an internal hardware fault.0x011B

Anyone experienced this before? Was it compensating to something external or did something fail internally?

Any help is appreciated.

Dan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

I pressed the power button and it started up without issue. There were no faults present when I looked in after the restart and it hasn't notified me of a problem since.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

Does your UPS utilize AVR often (often being majority of the day)? You can look in the log to see how often it reports "compensating for low or high input voltage" messages. The UPS is designed to use AVR every so often and not constantly so if it has been on very frequently, this could be a reason why it has failed. When it fails, it typically becomes welded or damaged somehow and would require the UPS to be replaced (either under warranty or not) assuming the UPS is a Smart UPS. Do you have any more information on the exact model of the UPS so that I could provide any additional feedback? And how old it is?

I could also review the full logs from your UPS Network Management Card to provide further feedback. (Instructions here- How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

The model number is SUM3000RMXL2U. It has only been deployed since October, 2013. There is no mention of low or high voltage inputs in the log. The only time it comes up is in the section of the Event log that I copied to the original post and the log still has data going back to October.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:08 AM . Last Modified: ‎2024-03-12 03:16 AM

Hmm,

How did you restart the UPS specifically? We might want to try and "braindead" it and observe and if that does not address it, the power module or the entire UPS may need to be replaced to address the fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

Angela,

I have a similar problem and it clears itself. Not sure why or how. It is a Smart-UPS 2200 RM. Should I be worried or replace the unit?

I am concerned with your comment "When it fails, it typically becomes welded or damaged somehow and would require the UPS to be replaced" which leads me to think it isn't properly sized to handle the added current when the voltage is low.

Regards,

J

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

Relays are electromechanical components and as such are subject to wearing out over time. The contacts inside are designed to handle X amount of current for Y amount of closing/opening cycles....over time the contact surfaces become pitted and the current carrying capacity becomes reduced, and what can happen concurrently is the return spring or solenoid mechanism inside becomes weakened. When a relay weld occurs its a combination of the weak return or the current itself passing across a smaller and smaller portion of clean metal on the two contacts that acts to bond the contacts together just like welding a two metal pieces - eg a cracked body panel on car.

The reason why Angela asked you why the UPS is going to AVR frequently - eg there is dirty power in the building and the UPS is sitting there clicking away several times a minute for hours on end - is that this is exactly what would cause the UPS's relays to wear out. Dirty power is something that many times needs to be looked into as it could be the result of failing or faulty equipment elsewhere in a facility.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

0 Likes
0
3599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:09 AM . Last Modified: ‎2024-03-12 03:16 AM

I pressed the power button and it started up without issue. There were no faults present when I looked in after the restart and it hasn't notified me of a problem since.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of