APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:19 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:35 AM . Last Modified: 2024-03-18 01:19 AM
Hi John -
Since this is a different issue, please open a new thread in the Back-UPS forum.
thanks,
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:19 AM
Bumping question
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:19 AM
apc does not even follow this forum anymore, lost interest in their products.
bye
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:34 AM . Last Modified: 2024-03-18 01:19 AM
Hi Davide -
I apologize for the delay. You can find a good explanation of Joules vs Let Through Voltage here:
http://www.apc.com/us/en/faqs/index?page=content&id=FA158814
Let through Voltage is a better measure of the quality of surge protection quality as Joule ratings can be artificially inflated without giving you any increase in protection. All of our surge products (whether stand alone or in a UPS) meet all industry standards for Surge Protection. The most important thing to remember is that not only can you get surge damage via power lines, but also via data cables. It is important to make sure that all possible points of entry are protected. We offer a variety of dataline surge products as well as power to ensure that you are properly protected.
In the future, if you need a reply quickly you can always contact our support team via phone, email, or chat.
Thanks,
Liam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:35 AM . Last Modified: 2024-03-18 01:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:35 AM . Last Modified: 2024-03-18 01:19 AM
Liam,
I can't tell by looking at any of the docs for your power strips or you UPSes that have data line coax protection if they will work with a cable modem that is DOCS v3.0..
My ups BE650 I loose 90% of my download speed if I use the data line protection for the coax line.
Please advise.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:35 AM . Last Modified: 2024-03-18 01:19 AM
Hi John -
Since this is a different issue, please open a new thread in the Back-UPS forum.
thanks,
Liam
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.