Strange sounds from Smart-UPS 1400

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Strange sounds from Smart-UPS 1400
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
haarp_apc
Crewman haarp_apc
Crewman

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:35 AM

0 Likes
6
2860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:35 AM

Strange sounds from Smart-UPS 1400

Hello there,

I recently got my hand on a Smart-UPS and intend to use it for my machines It's this one:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU1400RMI2U
I use the 230V version (European). It may be intended for racks, but that doesn't mean I have to mount it, does it? 😉

Well, since the batteries in this thing were swollen and completely dead, I got a new battery tray and connected it. To make sure that the batteries work fine and that this old unit still works fine, I connected the UPS output to a Variac with a hair dryer connected to it, so I can slowly ramp up the load and see how the UPS handles. Now, on AC this thing works like a charm (except for the transformer humming very loudly), but as soon as I switch to the batteries, I get a strange behavior. When the Variac goes over approx. 120V (should've been about 150-200W load), the UPS makes strange vibration noises, besides the humming. Because it's difficult to describe, I simply recorded it.
See attached file, strange sounds starting at 10s. the humming is also very load, especially on battery backup mode, but for some reason the mic didn't record that.

What could this be? I'm scared that this thing might blow apart or otherwise harm the attached hardware. Could it be that UPS don't like inductive loads like a Variac?
Thanks in advance!
And please, no "get a new one" posts, because I barely could afford even the batteries for this thing.

Message was edited by: haarp

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

Whatever works. 😉 Then again, I'd be careful with those instructions, since a) changing other settings in there can really screw up the UPS and b) there are different constants for each UPS. I wonder if they're out there on Google somewhere...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 10:12 PM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 10:12 PM

These units can be used as rack or tower configurations. Since it is the international model it requires international H,N,G three-wire 230v input. You mentioned 120v, which it should never receive. If it does this at 230v international with x% amount of load...that could be an inverter issue or, possibly the load I suppose. Smart-UPS are generally fairly tolerable of all but the most noisy motor-driven loads, or loads with very large amounts of feedback due to inefficiency or malfunction.

Reply

Link copied. Please paste this link to share this article on your social media post.

haarp_apc
Crewman haarp_apc
Crewman

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 10:11 PM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 10:11 PM

Hi,

The UPS was connected to 230V, like intended. But I plugged a variac (variable transformer) into the UPS output, which took 230V as input and output 120V to the load.

But I think I got it figured out. Some hair dryers seem to create A LOT of distortion because they use diodes when not running at full power. This was most probably the cause of the noises I heard from the UPS.


I've got another question. The UPS is running fine right now, but the remaining battery time is a bit strange. I'm using apcupsd to read that time. At 20% load, I've got about 30 minutes left (this itself is not even half of what the batteries should be able to endure) At 30% load it goes down to 16 mins and 8 mins at 40%. When I approach 50%, the runtime really starts to crumble, falling down to under 2 minutes. Theoretically, 2 times the load should merely half the runtime, not cut cut it in third or worse. Is the UPS really inefficient or why is this far from linear? Yes, I did a runtime calibration after changing the batts.

Message was edited by: haarp

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

Runtime isn't a linear equation. If you take a look at the runtime charts posted on the APC website, you'll see what I mean. But like you said, you should still be getting more runtime than that. Did you purchase APC batteries for replacements?

Reply

Link copied. Please paste this link to share this article on your social media post.

haarp_apc
Crewman haarp_apc
Crewman

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:33 AM

You're right, but they're close to linear 😉

As for the batteries...I have to admit that I bought my own. I mean, come on, APC slaps a sticker on it and sells them for 4x the price of the regular batts. I don't have that kind of money.
I just checked the real runtime. On a very high load, the UPS will immediately start beeping in 1s intervals to let me know that the runtime will soon be depleted. However, the device still runs for minutes and minutes.... Somethings wrong with the runtime calculation here.

Reply

Link copied. Please paste this link to share this article on your social media post.

haarp_apc
Crewman haarp_apc
Crewman

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:35 AM

0 Likes
0
2857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-02-14 02:35 AM

I have it figured out. I followed the procedure on this website:
http://www.joeteck.com/apc-repair.htm
and now the runtime seems more sane again. 🙂

But I'm curious. What is the background of this modification? What does it actually do?

edit: I found this:
" Explanation: The battery constants give the battery status via their
life expectancy. If the battery ages and is “exhausted”, the constant is
overwritten. The management software calculates the runtime of the UPS
with these constants. If the battery is now replaced, a self test must
be done with the new batteries. Through it, the red battery replace
indicator goes out and the battery constants should be reset to the
standard settings. This does not occur in some cases. Therefore, the
constants must be reset manually. "
http://lists.alioth.debian.org/pipermail/nut-upsdev/2006-June/000938.html

Message was edited by: haarp

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:47 PM . Last Modified: ‎2024-01-31 02:56 AM

Whatever works. 😉 Then again, I'd be careful with those instructions, since a) changing other settings in there can really screw up the UPS and b) there are different constants for each UPS. I wonder if they're out there on Google somewhere...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of