Symmetra RIM Faults

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RIM Faults
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
6
2363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

Symmetra RIM Faults

Symmetra Model SYAF16KRMI was Indicating bad RIM and replaced a new RIM, But still bad RIM is appearing .Now completely shutdown the symmetra and without redundancy each new RIM and existing IM working. When we insert redundancy unit it says RIM fault. Without redundancy raw data is O.K. But with redundancy you get raw data change @ RIM like (R 05 0000 0200 0000 0000 0000 E0F0 806B 2BF7E4F4 0183 D2AD )
And File was attached for your reference.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

Symmetra Model SYAF16KRMI was Indicating bad RIM and replaced a new RIM, But still bad RIM is appearing .Now completely shutdown the symmetra and without redundancy each new RIM and existing IM working. When we insert redundancy unit it says RIM fault. Without redundancy raw data is O.K. But with redundancy you get raw data change @ RIM like (R 05 0000 0200 0000 0000 0000 E0F0 806B 2BF7E4F4 0183 D2AD )
And File was attached for your reference.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

We brought new IM unit ,It was working fine,after ten days it's giving same error.( but now four battery modules are bad )
Powe veiw raw data is( R05 0000 0000 0200 0000 0000 E0E0 806B 2Bf7E0ECD 0187D6AD )

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

The raw status from your Redundant module does indicate the presence of at least one bad battery module in the system, but no other faults.

Do you have any other faults unrelated to the batteries?

I expect you have "Bad Battery Module, Main Frame R2, level 2 from top" (or some other location) and "Replace Batteries" in your fault and diagnostics menu. Are there other fault messages there?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-02-14 10:12 PM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-02-14 10:12 PM

Hi Bataya,

Thank you for providing the raw status data. It was very helpful in determining your issue.

The reason why there is no fault when only one SYMIM5 Intel Module is installed and the fault returns when the second SYMIM5 is installed is because there is a disagreement between the two modules.

Specifically, each module disagrees over its measurement of either Input/Output Voltage, Current, Frequency, or Power level. Since each module makes an independent assessment of the system's status, it is possible that one module is unable to accurately measure one of those 4 categories, resulting in a disagreement.

The best way to determine which module is bad is to record the voltage/current/frequency/load % from the status menu with just one module installed alone in the UPS.

Compare the measurements of both modules and you will likely find an obvious incorrect measurement.

This fault will always be reported by the module serving as the back-up, or redundant unit. It does NOT indicate that the module reporting the fault is the one that is bad.

Perhaps you could also provide the serial numbers and reported manufacturing date of your two Intel Modules. I think you will be able to easily identify the bad module by comparing their measurements.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

Hi Bataya,

I'm not sure what you mean. The raw data you provided indicates the issue I discussed in my previous post. Please let us know if you need assistance in determining which module is bad.

Generally, if you have a trusted module installed in the UPS and you install one of the new modules in the other bay, if the fault returns the new module you just installed is bad.

Reply

Link copied. Please paste this link to share this article on your social media post.

zolimar_apc
zolimar_apc
Cadet

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
0
2360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-02-14 02:33 AM

Can you help me please decoding my RAW date from the SYMIM5 Symmetra 16KVA MIM and RIM? Is there a description of the RAW data, which byte is what?

My both modules MIM and RIM since a few days are in fault (red LED on). On the RIM sometimes the LED go out, but usually it's ON.

Here are the data: both modules have f/w: 510 and slave 602, mfg date: 05/06/06.

MIM:

M05 0002 0000 0800 0000 0000 E0FE 006B 000FDDDB 01A7F5AD

RIM:

R05 0002 (sometimes changes to 0082) 0000 0800 0000 0000 E0FE 806B 23F7E4FE 0003D6AD

I also have a power unit SYPM4KI fault (f/w rev. 323, mfg date 05/20/06):

0804 4B26 0004 2086 0002 0C 46 7B 05 00 00 00 5B AC AC 01 05.

Do you know what is the root cause of it?

Thansk a lot,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
2361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:44 PM . Last Modified: ‎2024-01-31 02:56 AM

Symmetra Model SYAF16KRMI was Indicating bad RIM and replaced a new RIM, But still bad RIM is appearing .Now completely shutdown the symmetra and without redundancy each new RIM and existing IM working. When we insert redundancy unit it says RIM fault. Without redundancy raw data is O.K. But with redundancy you get raw data change @ RIM like (R 05 0000 0200 0000 0000 0000 E0F0 806B 2BF7E4F4 0183 D2AD )
And File was attached for your reference.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of