Hello,
I got some strange readings on my Symmetra LX 16 KVA unit yesterday. (Event log)
1) I got an APC InfraStruXure Manager reported an exceptions summary notification at 3/22/2009 @ 4:00:04 PM, it was reporting One or more faulty batteries exist, unit on bypass, and internal temp violation.
2) On 3/22/2009 @ 6:29:24 PM, the APC InfraStruXure Manager reported Faulty batteries no longer exist, No longer violates the Internal battery temperature threshold, and the UPS no longer on bypass in response to a hardware fault.
3) What would cause the above false entries? Can anything be done to prevent this?
(I have attached a copy of the log in MS Word format)
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Hi Mark
From your reported error logs, it seems that at least one battery was in the process of overheating. You may want to replace any other batteries of the same age, since if one battery has reached end-of-life, then it is very likely that another battery will soon do the same thing.
Also, installing a brand new battery in a system with low capacity/low performance old batteries will only diminish the new battery's useful life.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:47 PM
can you let us know what firmware is on the network management card inside the symmetra LX (this can be found by accessing the device and going to the administration->General->About menu)?
also, what version of ISX manager are you using (found in the Help->About menu in ISX manager)?
lastly, do these events show up in the network management card log of the Symmetra LX or did you just get emails about them? (it may be helpful to copy and paste this actual log to us as well)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
I'm sure I have a bad battery. The log shows bad battery, then the device drops off line, then recharges, dorps it's temp, then is good for a short period of time until it alerts as bad again.
I've attached a copy of my error log proving my point. A replacement battery is on order now, I can close this thread.
Thank you for your assistance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Thank you for your responses.
regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Hi Mark
From your reported error logs, it seems that at least one battery was in the process of overheating. You may want to replace any other batteries of the same age, since if one battery has reached end-of-life, then it is very likely that another battery will soon do the same thing.
Also, installing a brand new battery in a system with low capacity/low performance old batteries will only diminish the new battery's useful life.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:37 PM . Last Modified: 2024-03-14 11:46 PM
Yes, was a bad battery and it has since been replaced.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of