Posted: 2021-06-26 02:50 AM . Last Modified: 2024-03-19 01:49 AM
Please can someone help me with the startup process for new installation. After physical installation done I tried powering the UPS and a message on the screen says ''Communication lost, fault light ON, load light ON. I try to enter UPS configuration but assays 'Disconnected / initializing'.
I also need a direction to connect MBP INTERFACE BOARD AND EPO wiring oppositions board.
No Input/Output volts/Current kw display.
I will appreciate any, help to bring the system.
Thank you,
Oppong
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:50 AM . Last Modified: 2024-03-19 01:49 AM
Hi Bill,
Thank you very much for your response. The problem is resolved. Apparently I missed one o the terminators in from of the PDU unit. After correction everything seems to be fine.
I am very grateful.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:50 AM . Last Modified: 2024-03-19 01:49 AM
Hi,
Please contact local support for assistance with the start up of 3 phase UPS.
Local support contact information will be found at this link http://www.apc.com/gh/en/support/contact-us/index.jsp
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:50 AM . Last Modified: 2024-03-19 01:49 AM
Hi Bill,
Thank you very much for your response. The problem is resolved. Apparently I missed one o the terminators in from of the PDU unit. After correction everything seems to be fine.
I am very grateful.