SmartUps 30kVA In bypass
Hello,
I have a SmartUPS 30kVA and 3 power sources (1 mains, 1 500kVA day generator and 1 45kVA night generator). To comand the changeover i have 2 automatic transfer switchs.
The UPS was installed 1 week ago and after a changeover it goes to bypass mode with the information In bypass in response to an internal hardware fault.
After i restart the UPS it works fine.
Some useful information:
About UPS | |
Model: | Smart-UPS VT 30 kVA |
Serial Number: | PS1536230382 |
Firmware Revision: | 909.0718.I |
Manufacture Date: | 09/03/15 |
Status | |||
Last Battery Transfer: | Due to software command or UPS's test control | ||
Internal Temperature: | 30.0°C | ||
Runtime Remaining: | 27hr 11min | ||
Power | Phase L1 | Phase L2 | Phase L3 |
Input Voltage: | 215.0 VAC | 215.6 VAC | 216.3 VAC |
Bypass Input Voltage: | 215.9 VAC | 214.9 VAC | 216.0 VAC |
Output Voltage: | 219.7 VAC | 219.1 VAC | 219.3 VAC |
Current: | 00.00 Amps | 00.00 Amps | 00.00 Amps |
Input Frequency: | 50.02 Hz | ||
Load | Phase L1 | Phase L2 | Phase L3 |
Output Load: | 000.3 kVA | 000.1 kVA | 000.0 kVA |
Output Percent Load: | 003 %kVA | 001 %kVA | 000 %kVA |
Output Percent Power: | 002 %Watts | 000 %Watts | 000 %Watts |
Output Current: | 0001 Amps | 0000 Amps | 0000 Amps |
Output Frequency: | 50.21 Hz | ||
Battery | |||
Capacity: | 98.7 % | ||
Nominal Battery Voltage: | 192.0 VDC | ||
Actual Battery Bus Voltage: | 202.6 VDC | ||
Battery Current: | -0001.0 Amps | ||
External Battery Cabinet Rating: | 0000 | ||
Batteries: | 12 | ||
Bad Batteries: | 0 | ||
Intelligence Module | |||
Firmware Revision: | 07.18 | ||
Serial Number: | PS1536230382 | ||
Manufacture Date: | 09/03/15 | ||
Hardware Revision: | 1 |
m state: 09 02 02 02000038 00000000 00000001 03
Can someone help me?
Thanks
Nelson
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
Hi jon,
Thanks for the fast response.
Unfortunately im in africa and i can't contact the number ou gave me. Is there any international number? Or something i can do to try and diagnose what's wrong with my ups?
Thanks
Nelson
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:40 AM
Hi jon,
Thanks for the fast response.
Unfortunately im in africa and i can't contact the number ou gave me. Is there any international number? Or something i can do to try and diagnose what's wrong with my ups?
Thanks
Nelson