Hello,
We have a SURTD2200XLIM, It`s a new unit with 2 extra battery packs which I need to add in the UPS configuration (we installed a AP9613 unit in the UPS).
The unit has a RJ45 serial com connection and I use the 940-1525A communication cable that was delivered with the unit.
We tried bps 2400 and 9600 both with 8 data bits, parity none, stop bit 1, flow control none. Tried with 3 different laptops, one with USB to DB9 (others directly on DB9 on laptop), tested programs Hyperterminal and ADRCOM. Also tried braindeading the UPS to reset communications without luck.
On 1 laptop powerchute laptop is installed, UPS can communicate with server.
In Hyperterminal the screen remains blanck when the correct com port is selected (when wrong port is selected I see the commands I type).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:14 AM . Last Modified: 2024-03-18 03:41 AM
Jon,
Disconnecting the AP9613 did the trick, thank you!