SmartUPS RT 6000 XL Temperature Threshold max, high, low, min

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS RT 6000 XL Temperature Threshold max, high, low, min
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
3
2056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

SmartUPS RT 6000 XL Temperature Threshold max, high, low, min

Hey,

we just bought a "Smart-UPS RT 6000 XL" and are currently in the process to configure all of the connected machines.

Something I am currently struggling with, is the Point: "Configuration-> Universal i/o ,-> Temperature Threshold"

There I can set the temperature Thresholds: Max/ high/ low/ Minimum/ Hysteresis.

My Problem with that is:

in the PCNS there is only an option for "Temperature Probe 1 out of range"

Which range would that be? I hope it only executes a shutdown if the temperature is higher then the "Max temperature" configured on the UPS, or lower then the "Min Temperature" on the UPS.

Am I right?

I found this thread from 2013:

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/1651/config...

But there he reports a shutdown already gets triggered by PCNS when the "High temperature" is reached.

Any further info on that?

Regards

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi Sascha,

You can set Max and Min and yes, whatever happens first would trigger it (and you'd have those enabled for email notifications or alerts in the web UI of the NMC as well).

The ideal environment/ambient temperature for a UPS and the lead acid batteries would be something like 70-80ºF. (Some more general detail is here at the bottom -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156516 ) I would hope it doesn't get as hot as 113ºF (45ºC) but like you said, that should be a non issue and wea re only taking a precaution.

I don't really know what customers typically set to be completely honest but your thought process seems straight on based on a normal environment where a UPS is installed. I think we have some defaults in there too?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi,

This remains the same as to what Angela reported on the previous forum post. PCNS will react to which ever threshold is met first. An enhancement request has been entered and will be address in a future release of NMC firmware and PCNS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Okay, so best practice would be to not set the high and low temperature at all, but only set the Max and Min?

I was thinking to also set this max and min temp, so everything would safely shutdown incase our HVAC system breaks and the temperature gets to a critical level.

Any tips on what temperature would be best to set as the max/min temperature when all machines should be shutting down?

I was thinking about 45°C, since that is the temperature where I would guess the machines could get problems with.

Also I thought 45°C would be a good temperature for shutting down everything, because that is a temperature that cannot be reached accidentaly with our HVAC running, since the HVAC should keep the temperature at a maximum of 25°C and even on the hottest day the temperature shouldn't be able to rise above 30°C.

Also Min temperature, I was thinking about 7°C, since that would mean that we either got a breach to the outside world in winter (wall/door/windows/etc) or the HVAC system freaked out and cooled everything down too much.

What do you think about that? What would be best practice?

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi Sascha,

You can set Max and Min and yes, whatever happens first would trigger it (and you'd have those enabled for email notifications or alerts in the web UI of the NMC as well).

The ideal environment/ambient temperature for a UPS and the lead acid batteries would be something like 70-80ºF. (Some more general detail is here at the bottom -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156516 ) I would hope it doesn't get as hot as 113ºF (45ºC) but like you said, that should be a non issue and wea re only taking a precaution.

I don't really know what customers typically set to be completely honest but your thought process seems straight on based on a normal environment where a UPS is installed. I think we have some defaults in there too?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore