Smart-UPS X 3000 - Turned off and won't turn back on remotely

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000 - Turned off and won't turn back on remotely
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
5
2068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

Smart-UPS X 3000 - Turned off and won't turn back on remotely

APC | UPS Network Management Card 2

Not sure if anyone has seen this: Over the weekend this X3000 turn itself off. I now can remotely log into it but when I try to use the "turn-on" Controller I can't turn it back on.

Is this a known issue for this model unit?

HERE IS THE UPS INFO:

About UPS
 
Model: Smart-UPS X 3000
SKU: SMX3000RMLV2UNC
Firmware Revision: UPS 01.8 (ID10)
Manufacture Date: 08/22/2011
 
Apparent Power Rating: 2880 VA
Real Power Rating: 2700 W
 
Internal Battery SKU: RBC 117
External Battery SKU: RBC 118
 
   

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • smart-ups
  • x3000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

I was under the impression that the Battery was the issue but didn't know if there were any known factory issues with this unit

Thanks Angela!! What would this forum be without you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi,

When you go to Control - Outlet Groups what options are available? You should see On immediately and On with delay unless you are logged in a Read Only or Network Only user. If logged in as either of those you will need to change permissions to enable UPS control. If you go look in the NMC help file you will see a section on Configuration:Security:Local Users Management: General User.

SwTk%2F9rr9F%2BPkii4lflzAQ%3D%3D.pngSwTk%2F9rr9F%2BPkii4lflzAQ%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi Bill,

I logged into the UPS with the Super User Account and still didn't work. I contacted someone locally who DID turned it on for us. However this is strange because it is not the first time it happens on one of our X3000.

Now, I have tried to perform a battery test or runtime calibration and both failed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Hi Pavel,

Can you provide us with the event.txt log file or the .tar file dump from the NMC? That will be helpful to see if there is some sort of NMC->UPS communication problem if it is not a user permissions issue (and lack of permissions to control the UPS).

Instructions here on gathering the log files if you need them -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

Thanks!

I think part of what is going on is you have some battery issues that are preventing the UPS from operating/turning on normally. This appears to have started on May 12:

05/15/2015 09:18:04 Device UPS: The internal battery temperature no longer exceeds the critical threshold. 0x012D
05/15/2015 06:52:38 Device UPS: In bypass in response to an internal hardware fault. 0x011B
05/15/2015 06:52:33 Device UPS: The internal battery temperature exceeds the critical threshold. 0x012C
05/12/2015 05:07:03 Device UPS: No longer on battery power. 0x010A
05/12/2015 05:07:03 Device UPS: On battery power in response to distorted input. 0x0109

I think the UPS remained in bypass (so no battery back up power) and then:

06/06/2015 19:36:06 Device UPS: The output power is turned off. 0x0114
06/06/2015 19:36:06 Device UPS: No longer in bypass. 0x011E
06/06/2015 19:36:06 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
06/06/2015 19:36:06 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
06/06/2015 19:36:06 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135

I think on June 8th, someone was looking to get this on but the UPS failed its self test. Holding the on button likely forced it on:

06/08/2015 11:01:07 Device UPS: failed a self-test. 0x0106
06/08/2015 11:01:06 Device UPS: At least one faulty battery exists. 0x0119
06/08/2015 11:01:05 Device UPS: Started a self-test. 0x0137

It seems as though the unit is from 2011 and the battery is from 2012? 

BatteryDate=08/15/2012 (from config.ini)

Long story short, I think you need a replacement internal battery and that will clear up these issues and the UPS will operate normally.

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
2067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:51 PM . Last Modified: ‎2024-03-01 12:21 AM

I was under the impression that the Battery was the issue but didn't know if there were any known factory issues with this unit

Thanks Angela!! What would this forum be without you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore