Power pack for SMX2200HV

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power pack for SMX2200HV
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
4
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

Power pack for SMX2200HV

Dear Forum members, I have a rack mounted SMX2200HV Smart UPS but it's internal batteries runs out so first than before, I wish to buy an external power pack and connect it to this device, May I know if this is applicable? if yes which model should I go for?  Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • back-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

The APC product page for the SMX2200HV lists the SMX120BP external battery pack (under Options / Batteries / Smart-UPS Battery Systems). Is that the sort of thing you were asking about? Or do you mean that the battery in the SMX2200HV doesn't last as long as it used to? If that's what you meant, and the load has remained the same, then you might just need a replacement battery, which would appear to be the RBC143.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

The SMX120BP I linked to in my first reply seems to be the official way to add battery capacity to your UPS. If the internal battery pack is bad, you should probably replace that first to see if you get sufficient runtime that way. If you're talking about adding a bunch of generic non-APC batteries, that wouldn't be warranted/supported by APC. [I don't work for APC, by the way.] I would caution you that your UPS has a high-voltage battery bus that can be dangerous if you come into contact with it while energized.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

The APC product page for the SMX2200HV lists the SMX120BP external battery pack (under Options / Batteries / Smart-UPS Battery Systems). Is that the sort of thing you were asking about? Or do you mean that the battery in the SMX2200HV doesn't last as long as it used to? If that's what you meant, and the load has remained the same, then you might just need a replacement battery, which would appear to be the RBC143.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

Thanks Terry,  Actually i wanted to know whether this type of UPS accept external battery packs, if it does, how can i get it and how do i hook it to the main UPS? otherwise if thats not possible i will go for the option of replacing the batteries in the internal cattridge. 

Regards, Henry 

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

The SMX120BP I linked to in my first reply seems to be the official way to add battery capacity to your UPS. If the internal battery pack is bad, you should probably replace that first to see if you get sufficient runtime that way. If you're talking about adding a bunch of generic non-APC batteries, that wouldn't be warranted/supported by APC. [I don't work for APC, by the way.] I would caution you that your UPS has a high-voltage battery bus that can be dangerous if you come into contact with it while energized.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

0 Likes
0
1567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:50 PM . Last Modified: ‎2024-03-01 12:21 AM

Thanks for everything!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore