Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
I have an SMX1500RMI2U + 1x SMX48RMBP2U. It's currently backing up a home theatre system that draws no more than 250W. I based my purchase on the runtime chart of the product site suggesting that at this load, I should be getting around 3 hours of runtime. When the unit arrived 6 months ago, I was getting almost exactly that. Now, I'm barely getting 2 hours. I understand that the runtime chart isn't a set of hard and fast rules. But a 1 hour delta seems a bit much. Any ideas what the problem could be ? It's happy with its own self test
Firmware : 09.8 ID:20
Local Power Quality set to Poor to maximise runtime
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
Hi Voidstar
I appreciate the comeback. I managed to contact APC via the website and they've graciously agreed to swop out the unit. I used the same description of the problem ( as above ) and added only the serial number of unit. So there must be an issue with a batch or thereabouts
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
I don't know if 3hr -> 2hr decline in runtime over a year is typical -- maybe someone else can chime in.
Just wanted to say that batteries are a consumable. The more often and deeper they are discharged, the shorter the runtime will be. Discharging every day, for instance, will quickly ruin them. On the other hand, runtime is estimated based on discharge so if you haven't discharged the battery much, you may need to do a runtime calibration to get a more accurate estimate.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:51 PM . Last Modified: 2024-03-01 12:21 AM
Hi Voidstar
I appreciate the comeback. I managed to contact APC via the website and they've graciously agreed to swop out the unit. I used the same description of the problem ( as above ) and added only the serial number of unit. So there must be an issue with a batch or thereabouts
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.