SmartUPS RT 3000 not change status after power failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS RT 3000 not change status after power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

0 Likes
4
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

SmartUPS RT 3000 not change status after power failure

Hi all,
I've a SmartUPS RT 3000 ad powerchute 9.01. I can connect to power unit
in Simple Mode on /dev/ttyS0 and to see in log "Connection Established"
The problem is that when I simulate power failure, the state of UPS
remain in "On line" and so no action go on !
It seems that PowerChute can see device but can't comunicate with
UPS .... and so can't recognize "power Failure"..

UPS model: SmartUPS RT3000
Serial Cable model (provided by APC): 940-1525A
OS: Linux RedHat enterprise 5

Thanks in advance,
Gianni

Message was edited by: gioklr

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:34 AM

No, I've only 940-1524A : I don't know if it is different from 940-1524.
In any case w'll try with 940-0024 but we must wait ... we are looking on the web for buy it !
I'll inform you on the response of it .
Thanks for your interest !

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

when you installed PCBE, in what mode did you install it? did you have the software auto-detect your UPS? it seems like you somehow installed this within simple signaling mode and it should be in smart. do you see any status info within PCBE like input voltage or battery capacity?


can you tell us what you see when you login to the powerchute agent and click on server shutdown->system settings?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

Hi,first of all
thanks for your answer.
Yes , I tried "smart" connection, but it didn't work at all: In this connection
mode PCBE didn't identify the UPS (it mark UPS as Unknown)
In attach you can find the screenshot of "System Setting" page.

We are thinking to change cable: in readme file they suggest 940-0024 or 940-0020
...but i'm not sure this fix the problem !

This is wath I've done after ...
American Power Conversion
PowerChute Business Edition Agent Configuration Utility
------------------------------------------------------------

Username

poweruser
Password
>
Would you like to change the current username? (Yes or No)
No
Would you like to change the current password? (Yes or No)
No
Select the Signal Type
[1]: Smart
[2]: Simple
[3]: SMX, SMT, SURTD (Smart Signalling)
1
Select the serial port
[1]: /dev/ttyS0
[2]: /dev/ttyS1
[3]: Other
1
Signal Type: Smart
Share UPS: No
Serial Port: /dev/ttyS0

Are the UPS settings correct? (Yes or No)
Yes
Start PowerChute Business Edition Agent? (Yes or No)
>
Yes
PowerChute Business Edition started.

..in second attach file (ups_02.jpg) there is the unknown UPS system !


Thanks,
Gianni

Message was edited by: gioklr

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:35 AM

940-0024 is what you need or even 940-1524 (15 foot version).

we definitely need to be using smart signaling so somehow it is going to simple. so let's force it to smart and then make sure you do NOT use the 940-0020 because thats simple signaling only. do you have a 940-0024 or 940-1524 black cable? the 20 cable is gray.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:34 AM

0 Likes
0
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:42 AM . Last Modified: ‎2024-03-06 02:34 AM

No, I've only 940-1524A : I don't know if it is different from 940-1524.
In any case w'll try with 940-0024 but we must wait ... we are looking on the web for buy it !
I'll inform you on the response of it .
Thanks for your interest !

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore