Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SmartUPS 750 - PowerChute Business - Win10 and 64bit
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2905:52 AM. Last Modified: 2024-03-1312:23 AM
SmartUPS 750 - PowerChute Business - Win10 and 64bit
Ok - I have run PowerChute Business on this SmartUPS for several years. I went to use it and thought I had simply forgotten my password. I then followed the guideline to uninstall/reinstall PowerChute Business, I have the CD for V8.5.1. That reinstallation went ok, and the UPS system was found on the USB. But, I still could not use the Agent to connect. It did not respond when I entered the user name/password just configured. I noted the following
NOTE: The PowerChute Business Edition web interface requires the Sun Microsystems 1.4.2 32-bit JVM or higher plug-in for your 32-bit web browser. 64-bit web browser or JVM is not supported.
This is a 64bit system, running Wni10.
I then downloaded Version 9.2 and attempted to update - it gets to an unable to locate UPS then gives an option if the UPS has a DB9 or RJ11 connector. My SmartUPS is USB connected. The update fails at this point, trying either DB9 or RJ11 results in failure.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2905:52 AM. Last Modified: 2024-03-1312:23 AM
Hi,
Uninstall the 8.5.1 version then run the 9.2 installer. If the UPS is not automatically discovered select DB9 if the Smart-UPS is a SU, SUA model. If the Smart-UPS is a SMT, or SMX model select RJ45. You can also run the PowerChute Agent installer and skip the initial auto discovery. See FAQ FA159703 and review the attached video.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2905:52 AM. Last Modified: 2024-03-1312:23 AM
Hi,
Uninstall the 8.5.1 version then run the 9.2 installer. If the UPS is not automatically discovered select DB9 if the Smart-UPS is a SU, SUA model. If the Smart-UPS is a SMT, or SMX model select RJ45. You can also run the PowerChute Agent installer and skip the initial auto discovery. See FAQ FA159703 and review the attached video.
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.