A few questions re: the SURTD5000RMXLP3U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • A few questions re: the SURTD5000RMXLP3U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
3
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

A few questions re: the SURTD5000RMXLP3U

Hi, I'm building out a small server room for a new home and the SURTD5000RMXLP3U looks like a great fit for my server rack. I have a few questions about it:

- The specs say it supports 208V and 120V output; I assume it can do that simultaneously, is that correct? Most of my computers and networking gear can run at 208V, but I may have one or two devices that need 120V, and I want to make sure I can rack them in the same enclosure.

- With no load, what's the approximate power usage of the SURTD5000RMXLP3U?

- An EPO connection is optional, correct?

Thanks in advance; this forum looks like a fantastic resource and it's great to see a company like APC/Schneider offering this kind of support!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

hello. i'll try to help answer.

  1. Yes, same time - if you look at the rear seen here -> SURTD5000RMXLP3U - More Images - it shows some 120V receptacles right on it along with some 208V ones which you may need to get a Rack PDU for to give you additional 208V outlets.
  2. Based on the online thermal dissipation value listed of 1589 and knowing 1 watt = 3.41BTU, that gives me about ~466 watts you could expect worst case.
  3. If you look at that same picture I posted above, there is actually a EPO terminal already on the UPS. It is on the bottom towards the right and lime green in color. More information in the user's guide on that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

hello. i'll try to help answer.

  1. Yes, same time - if you look at the rear seen here -> SURTD5000RMXLP3U - More Images - it shows some 120V receptacles right on it along with some 208V ones which you may need to get a Rack PDU for to give you additional 208V outlets.
  2. Based on the online thermal dissipation value listed of 1589 and knowing 1 watt = 3.41BTU, that gives me about ~466 watts you could expect worst case.
  3. If you look at that same picture I posted above, there is actually a EPO terminal already on the UPS. It is on the bottom towards the right and lime green in color. More information in the user's guide on that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:22 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:22 AM

Hi Angela,

Thanks for the very speedy response. Again, this is such a great resource.

Re: the EPO connection, I wasn't clear what I meant: I know there's a terminal on the UPS, but what I meant is, the UPS will operate even if the EPO terminal is not connected to an EPO switch, correct?

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:22 AM

0 Likes
0
812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:22 AM

You're very welcome. I am glad people like our community and can count on it as a resource.

And yes, EPO is optional - no requirement for you to have one unless required by your local code of course.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore