Smart-UPS RT 5000 XL: A battery bus soft start fault no longer exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 XL: A battery bus soft start fault no longer exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
4
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

Smart-UPS RT 5000 XL: A battery bus soft start fault no longer exists

Hi,

I am receiving below alert  Smart-UPS RT 5000 XL: A battery bus soft start fault no longer exists.?

Could any one let us know about it.


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

01/25/2015 10:40:20 System: NTP update successful.
 01/24/2015 10:40:15 System: NTP update successful.
 01/23/2015 19:57:33 UPS: In bypass in response to an internal hardware fault.
 01/23/2015 19:57:33 UPS: A battery bus soft start fault exists.
 01/23/2015 10:40:11 System: NTP update successful.
 01/22/2015 10:40:06 System: NTP update successful.
 01/21/2015 10:40:01 System: NTP update successful.
 01/20/2015 10:39:56 System: NTP update successful.
 01/19/2015 10:39:51 System: NTP update successful.
 01/18/2015 10:39:47 System: NTP update successful.
 01/17/2015 10:39:42 System: NTP update successful.
 01/16/2015 10:39:37 System: NTP update successful.
 01/15/2015 10:39:32 System: NTP update successful.
 01/14/2015 10:39:27 System: NTP update successful.
 01/13/2015 10:39:23 System: NTP update successful.
 01/12/2015 10:39:18 System: NTP update successful.
 01/11/2015 10:39:13 System: NTP update successful.
 01/10/2015 10:39:07 System: NTP update successful.
 01/09/2015 14:01:43 UPS: passed a self-test.
 01/09/2015 14:01:34 UPS: Started a self-test.
 01/09/2015 10:39:03 System: NTP update successful.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 01/08/2015 21:12:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 01/08/2015 21:12:23 UPS: Restored the local network management interface-to-UPS communication.
 01/08/2015 21:12:01 System: Network service started. IPv6 address FE80::2C0:B7FF:FE5B:4AE3 assigned by link-local autoconfiguration.
 01/08/2015 21:11:57 System: Network service started. System IP is 156.127.161.248 from manually configured settings.
 01/08/2015 21:11:51 System: Warmstart.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

can you post the entire data.txt and event.txt log so we can get a better understanding of what is happening with the UPS?

these logs can be downloaded via FTP from your network management card where the alerts are coming from. instructions are in our knowledge base (FAQ) in article ID FA156131.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

Hi Angela,

I have a Smart-UPS X 3000 with the same error:

  Critical Alarm 1 Critical Alarm Present

◾Battery Bus Soft Start Fault


And the status look good:

***

Status Smart-UPS X 3000

 

Last Battery Transfer: None

Internal Temperature: 22.3°C

Runtime Remaining: 2hr 6min 20sec

UPS Input    

Input Voltage: 240.0 VAC @ 50.1 Hz 

 

UPS Output  

Output Voltage: 240.0 VAC @ 50.1 Hz

Load Current: 0.8 Amps

 

Output VA: 6.9 %

Output Watts: 7.6 %

Output Efficiency: 87.6 %

Output Energy Usage: 1410.85 kWh

Battery Status  

Battery Capacity: 100.0 %

Battery Voltage: 53.9 VDC

Num of External Batteries: 0 

***

Can you help me to fix this issue? Thank you in advance.

Regards,

Vuong

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

Your UPS and the original poster's UPS are different models. on SURT, sometimes this can be related to a bad battery but on SMX it is generally a hardware fault.

Could you provide the log files I requested from the original poster? I'll take a look and see if anything else jumps out at me.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

0 Likes
0
2852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:52 AM . Last Modified: ‎2024-03-13 12:23 AM

01/25/2015 10:40:20 System: NTP update successful.
 01/24/2015 10:40:15 System: NTP update successful.
 01/23/2015 19:57:33 UPS: In bypass in response to an internal hardware fault.
 01/23/2015 19:57:33 UPS: A battery bus soft start fault exists.
 01/23/2015 10:40:11 System: NTP update successful.
 01/22/2015 10:40:06 System: NTP update successful.
 01/21/2015 10:40:01 System: NTP update successful.
 01/20/2015 10:39:56 System: NTP update successful.
 01/19/2015 10:39:51 System: NTP update successful.
 01/18/2015 10:39:47 System: NTP update successful.
 01/17/2015 10:39:42 System: NTP update successful.
 01/16/2015 10:39:37 System: NTP update successful.
 01/15/2015 10:39:32 System: NTP update successful.
 01/14/2015 10:39:27 System: NTP update successful.
 01/13/2015 10:39:23 System: NTP update successful.
 01/12/2015 10:39:18 System: NTP update successful.
 01/11/2015 10:39:13 System: NTP update successful.
 01/10/2015 10:39:07 System: NTP update successful.
 01/09/2015 14:01:43 UPS: passed a self-test.
 01/09/2015 14:01:34 UPS: Started a self-test.
 01/09/2015 10:39:03 System: NTP update successful.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 01/08/2015 21:12:25 UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 01/08/2015 21:12:23 Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 01/08/2015 21:12:23 UPS: Restored the local network management interface-to-UPS communication.
 01/08/2015 21:12:01 System: Network service started. IPv6 address FE80::2C0:B7FF:FE5B:4AE3 assigned by link-local autoconfiguration.
 01/08/2015 21:11:57 System: Network service started. System IP is 156.127.161.248 from manually configured settings.
 01/08/2015 21:11:51 System: Warmstart.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore