SmartUPS 2200XL wrong wattage in gapcmon??

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 2200XL wrong wattage in gapcmon??
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

0 Likes
4
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

SmartUPS 2200XL wrong wattage in gapcmon??

Hi All

I put new batteries in two weeks ago to correct the all flashing battery graph and it didn't fix it so today I ran the calibration and it seems to be taking, that's one problem fixed but I noticed it's not reporting the wattage correctly.

DATE     : 2017-03-01 12:02:06 -0800  
HOSTNAME : localhost.localdomain
VERSION  : 3.14.12 (29 March 2014) redhat
UPSNAME  : localhost.localdomain
CABLE    : USB Cable
DRIVER   : USB UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2017-03-01 11:14:27 -0800  
MODEL    : Smart-UPS 2200 RM XL
STATUS   : ONLINE
LINEV    : 116.6 Volts
LOADPCT  : 58.5 Percent
BCHARGE  : 66.0 Percent
TIMELEFT : 9.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
OUTPUTV  : 116.6 Volts
SENSE    : Low
DWAKE    : -1 Seconds
DSHUTD   : 180 Seconds
LOTRANS  : 106.0 Volts
HITRANS  : 127.0 Volts
RETPCT   : 0.0 Percent
ITEMP    : 23.8 C
ALARMDEL : 30 Seconds
BATTV    : 54.8 Volts
LINEFREQ : 60.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT  : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI   : 7 days
STATFLAG : 0x05000008
MANDATE  : 2006-04-22
SERIALNO : JS0617037870
BATTDATE : 2017-02-14
NOMOUTV  : 120 Volts
NOMBATTV : 48.0 Volts
FIRMWARE : 690.16.D USB FW:7.2
END APC  : 2017-03-01 12:02:59 -0800  

The problem is that gapcmon is reporting the wattage as 351 of 600 Watts. The ratio is about right since apcstatus reports load at 58.5 percent but why is it incorrectly reporting 600Watts instead of 2200?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

Hi All

I talked to Advanced Tech Support and my Battery Constant was supposed to be 81. I managed to change mine without bricking my unit and now my run time is 21 minutes which is more in line with what I expected. If you're not familiar with terminals, serial ports and RS232 I wouldn't recommend trying to change it yourself.

Thanks APC/Schneider - great customer service!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

We don't directly support gapcmon, but if you have the ability to terminal into the UPS using a serial connection we could verify whether or not the UPS is providing the proper data. You would need an APC Smart Signaling serial cable (#940-0024 or #940-1524) and a computer running a terminal app such as HyperTerminal. Given that your UPS is 10 years old and does not have upgradable  firmware, there would not be anything we could do if it is reporting incorrect data, but you would at least know that it is the UPS and not the software.

Either way, this is a cosmetic issue and would not affect the performance of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

OK, Life is busy and I just got around to pulling that rack and installing the proper cable.

Now when I connect with the terminal it will respond SM (to Y)

J returns 013 - That's got to be wrong, 13 minutes on a fresh set of batteries?

1-1 returns PROG and 0 returns a battery contant of 65.

Can anyone tell me the correct Battery constant for an SUA2200RMXL3U?

Jeff

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:46 AM . Last Modified: ‎2024-03-18 03:16 AM

Hi All

I talked to Advanced Tech Support and my Battery Constant was supposed to be 81. I managed to change mine without bricking my unit and now my run time is 21 minutes which is more in line with what I expected. If you're not familiar with terminals, serial ports and RS232 I wouldn't recommend trying to change it yourself.

Thanks APC/Schneider - great customer service!

Reply

Link copied. Please paste this link to share this article on your social media post.

hulubei
Crewman hulubei
Crewman

Posted: ‎2023-04-02 01:00 AM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-02 01:00 AM

Hello,

My SUA 1500VA is showing in PowerChute like being 3000RM. Of course, mine is having only 2 batteries, not 4. Hence, it will throw constantly battery error and also a strange 54.4v although it's not possible to get to this value from only 2 batteries.

Who can help me to make up with his mind and think at itself in the proper way like being an 1500 VA unit instead of 3000VA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of