One of the battery packs in my SmartUPS 2200 failed. I replaced it and every thing worked well for a while. The the battery charge indicator lights then started flashing. I replaced the other battery pack and the problem did not go away.
When I take all the load off the UPS, the flashing stops. Do I need to remove the controller board(s) and send them to a service center? If So, can someone point me in the right direction?
Thanks,
Bill Mahaffey
319 Roundabout Drive
Trussville, Alabama
wmahaffey@centurytel.net
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Bill,
Call into support or email support and request a calibration key.
That'll solve your problem.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Thanks,
Bill
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Bill,
Call into support or email support and request a calibration key.
That'll solve your problem.