SmartUPS 1400 battery lights flashing simultaneously

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 1400 battery lights flashing simultaneously
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:12 AM

0 Likes
5
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:12 AM

SmartUPS 1400 battery lights flashing simultaneously

I have a SmartUPS 1400 with all 5 battery charge lights flashing simutanelously. I didn't see any thing referring to this in the manual.
The 3 lights ( Overload, On battery, replace battery) next to them are flashing very dimly. The ups was run down over Hurricane Ike. It has been running properly with 6 devices plugged in. The load has 3 lights lit up (50%). Any input?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

Hi,

Please see Schneider Electric FAQ FA265136 "Why are all LED's flashing simultaneously on my Smart-UPS SU, SUA, or SURT model?"

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

[take a look here|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1497]

the quick version:

essentially this means that your runtime is probably getting low. the LEDs flashing are telling you that you runtime on battery is within 2 minutes of your low battery signaling time (which is a default of 2 minutes from the factory - so it'd be telling you that you only have 3-4 minutes of runtime). so i'd check your runtime remaining if you use software with this UPS (which would be Powerchute business edition.) the batteries last on average from 3-5 years depending on usage and environment. if you are within this time frame since your last battery replacement, you probably want to start thinking about getting some replacement batteries.

if your batteries are new, then you can do one of two things: 1.) do a manual runtime calibration as mentioned in the link above to calibrate the UPS so it knows you have new batteries with runtime or 2.) since it is an 1400 VA UPS, it must be an SU1400. any model beginning with SU can use what we call a calibration key which plugs into the serial port and will recalibrate the UPS's runtime within a couple seconds. i recommend this option but only AFTER you purchase new batteries. if your batteries are old and you get one of these then the runtime will not be accurate at all.

so, if you decide you need replacement batteries and you replace the batteries and the LEDs are still flashing, then you can either email or call APC tech support and simply request a calibration key which we can send to you. it will come with instructions on what to do and will talk all of 3 minutes to complete and you wont have to go through the hassle of the manual runtime calibration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

So basically this is a warning you would receive before the replace Battery Light is on? I am not sure of the age of the batteries. I am assuming they are older. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

it can be. low runtime could be the cause of a very high load on the UPS as well in conjuction with a low battery signaling time you have adjusted too high.

you can check the serial # on the UPS to find the age of the UPS if they are the original batteries (if you think they are).

JS0112 is an example of the first portion of an APC serial number. the 00 means the UPS was manufactured in the year 2001 and the 12 indicates it was the 12th week of the year 2001.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

I have APC Smart UPS 1400 and Got an error when I plug in the UPS with power and click the Power button all the center lights start Blinking.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:08 AM . Last Modified: ‎2024-03-08 03:11 AM

Hi,

Please see Schneider Electric FAQ FA265136 "Why are all LED's flashing simultaneously on my Smart-UPS SU, SUA, or SURT model?"

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now