Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
Hi,
What's the problem with Smart UPS 1000VA when the 5 LEDs Battery Charge keeps flashing simultaneously. But sometimes in between, the LEDs lights are stable.
I read through the manual and could suggest the UPS operating temperature / environment may not be well conditions. But I don't think so, as it is an aircon room and also having another 2200VA UPS with no such problems.
Many thanks.
Regards,
Daryl
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
It means the UPS's available runtime is significantly low. If you recently replaced the battery, contact support for options to resolve that. If you haven't replaced the battery, this would be a good indicator.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:08 AM . Last Modified: 2024-03-08 03:11 AM
It means the UPS's available runtime is significantly low. If you recently replaced the battery, contact support for options to resolve that. If you haven't replaced the battery, this would be a good indicator.