Smart-ups RT10000 not charging battery and always beep

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-ups RT10000 not charging battery and always beep
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
6
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

Smart-ups RT10000 not charging battery and always beep

Hi

i have APC smart-ups RT10000 always beep every 2 second and red flash light for battery fault is on . i checked the all 4 battery inside all gives 108 v DC foe each battery which is correct for total volts but the smart-ups keep beep every 2 second i re move all the battery and reinstall them again .. but no luck
i open the 4 battery from inside and found 8 small battery 12 v dc inside all connected together each one of them give 13.5 volt and all give 108 volt total
i power off the smart-ups rt10000 and power on again .. beep and red flash light still there ........ even if turn the switch to bypass the battery also no luck

could you please help me to find out what is the problem ?

best regards

adly

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

this is the log file

Date Time Event
Date Time Event
09/11/2012 09:25:27 UPS: The battery is not installed properly.
09/11/2012 09:25:11 UPS: The battery is now installed.
09/11/2012 09:24:54 UPS: The battery is not installed properly.
09/11/2012 09:24:36 UPS: The battery is now installed.
09/11/2012 09:23:47 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:21:04 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:17:10 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:15:31 UPS: The battery is not installed properly.
09/11/2012 09:15:13 UPS: The battery is now installed.
09/11/2012 09:14:21 UPS: The battery is not installed properly.
09/11/2012 09:13:47 UPS: The battery is now installed.
09/11/2012 09:10:41 UPS: The battery is not installed properly.
09/11/2012 09:10:23 UPS: The battery is now installed.
09/11/2012 09:04:58 UPS: The battery is not installed properly.
09/11/2012 09:04:41 UPS: The battery is now installed.
09/11/2012 08:59:17 UPS: The battery is not installed properly.
09/11/2012 08:59:00 UPS: The battery is now installed.
09/11/2012 08:58:25 UPS: The battery is not installed properly.
09/11/2012 08:58:09 UPS: The battery is now installed.
09/11/2012 08:57:53 UPS: The battery is not installed properly.
09/11/2012 08:57:35 UPS: The battery is now installed.
09/11/2012 08:55:52 UPS: The battery is not installed properly.
09/11/2012 08:55:35 UPS: The battery is now installed.
09/11/2012 08:54:44 UPS: The battery is not installed properly.
09/11/2012 08:54:27 UPS: The battery is now installed.
09/11/2012 08:53:02 UPS: The battery is not installed properly.
09/11/2012 08:52:43 UPS: The battery is now installed.
09/11/2012 08:26:43 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:23:14 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:19:09 UPS: The battery is not installed properly.
09/11/2012 08:18:53 UPS: The battery is now installed.
09/11/2012 07:33:04 UPS: The battery is not installed properly.
09/11/2012 07:32:46 UPS: The battery is now installed.
09/11/2012 07:31:03 UPS: The battery is not installed properly.
09/11/2012 07:30:48 UPS: The battery is now installed.
09/11/2012 07:29:22 UPS: The battery is not installed properly.
09/11/2012 07:29:04 UPS: The battery is now installed.
09/11/2012 07:28:47 UPS: The battery is not installed properly.
09/11/2012 07:28:14 UPS: The battery is now installed.
09/11/2012 07:27:22 UPS: The battery is not installed properly.
09/11/2012 07:27:05 UPS: The battery is now installed.
09/11/2012 07:22:33 UPS: The battery is not installed properly.
09/11/2012 07:21:59 UPS: The battery is now installed.
09/11/2012 07:17:26 UPS: The battery is not installed properly.
09/11/2012 07:17:07 UPS: The battery is now installed.
09/11/2012 07:15:59 UPS: The battery is not installed properly.
09/11/2012 07:15:43 UPS: The battery is now installed.
09/11/2012 07:15:26 UPS: The battery is not installed properly.
09/11/2012 07:14:51 UPS: The battery is now installed.
09/11/2012 07:14:34 UPS: The battery is not installed properly.
09/11/2012 07:14:18 UPS: The battery is now installed.
09/11/2012 07:13:26 UPS: The battery is not installed properly.
09/11/2012 07:13:08 UPS: The battery is now installed.
09/11/2012 07:12:17 UPS: The battery is not installed properly.
09/11/2012 07:12:01 UPS: The battery is now installed.
09/11/2012 07:07:10 UPS: The battery is not installed properly.
09/11/2012 07:06:54 UPS: The battery is now installed.
09/11/2012 07:05:11 UPS: The battery is not installed properly.
09/11/2012 07:04:21 UPS: The battery is now installed.
09/11/2012 07:03:29 UPS: The battery is not installed properly.
09/11/2012 07:02:20 UPS: The battery is now installed.
09/11/2012 07:02:03 UPS: The battery is not installed properly.
09/11/2012 07:01:45 UPS: The battery is now installed.
09/11/2012 06:59:47 UPS: The battery is not installed properly.
09/11/2012 06:59:30 UPS: The battery is now installed.
09/11/2012 06:58:37 UPS: The battery is not installed properly.
09/11/2012 06:58:22 UPS: The battery is now installed.
09/11/2012 06:56:39 UPS: The battery is not installed properly.
09/11/2012 06:56:04 UPS: The battery is now installed.
09/11/2012 06:54:56 UPS: The battery is not installed properly.
09/11/2012 06:54:40 UPS: The battery is now installed.
09/11/2012 06:54:06 UPS: The battery is not installed properly.
09/11/2012 06:52:24 UPS: The battery is now installed.
09/11/2012 06:50:57 UPS: The battery is not installed properly.
09/11/2012 06:50:08 UPS: The battery is now installed.
09/11/2012 06:49:51 UPS: The battery is not installed properly.
09/11/2012 06:49:33 UPS: The battery is now installed.
09/11/2012 06:47:15 UPS: The battery is not installed properly.
09/11/2012 06:44:58 UPS: The battery is now installed.
09/11/2012 06:44:08 UPS: The battery is not installed properly.
09/11/2012 06:43:52 UPS: The battery is now installed.
09/11/2012 06:43:18 UPS: The battery is not installed properly.
09/11/2012 06:42:59 UPS: The battery is now installed.
09/11/2012 06:42:42 UPS: The battery is not installed properly.
09/11/2012 06:42:26 UPS: The battery is now installed.
09/11/2012 06:42:09 UPS: The battery is not installed properly.
09/11/2012 06:41:51 UPS: The battery is now installed.
09/11/2012 06:40:09 UPS: The battery is not installed properly.
09/11/2012 06:39:52 UPS: The battery is now installed.
09/11/2012 06:39:35 UPS: The battery is not installed properly.
09/11/2012 06:39:18 UPS: The battery is now installed.
09/11/2012 06:38:26 UPS: The battery is not installed properly.
09/11/2012 06:38:11 UPS: The battery is now installed.
09/11/2012 06:37:01 UPS: The battery is not installed properly.
09/11/2012 06:36:11 UPS: The battery is now installed.
09/11/2012 06:33:37 UPS: The battery is not installed properly.
09/11/2012 06:33:03 UPS: The battery is now installed.
09/11/2012 06:31:55 UPS: The battery is not installed properly.
09/11/2012 06:31:48 UPS: A discharged battery condition no longer exists.
09/11/2012 06:31:20 UPS: The battery is now installed.
09/11/2012 06:31:03 UPS: The battery is not installed properly.
09/11/2012 06:30:47 UPS: The battery is now installed.
09/11/2012 06:29:21 UPS: The battery is not installed properly.
09/11/2012 06:29:04 UPS: The battery is now installed.
09/11/2012 06:26:30 UPS: The battery is not installed properly.
09/11/2012 06:26:13 UPS: The battery is now installed.
09/11/2012 06:25:38 UPS: The battery is not installed properly.
09/11/2012 06:25:05 UPS: The battery is now installed.
09/11/2012 06:21:05 UPS: The battery is not installed properly.
09/11/2012 06:20:15 UPS: The battery is now installed.
09/11/2012 06:19:06 UPS: The battery is not installed properly.
09/11/2012 06:18:49 UPS: The battery is now installed.
09/11/2012 06:18:33 UPS: The battery is not installed properly.
09/11/2012 06:17:42 UPS: The battery is now installed.
09/11/2012 06:16:16 UPS: The battery is not installed properly.
09/11/2012 06:15:59 UPS: The battery is now installed.
09/11/2012 06:15:42 UPS: The battery is not installed properly.
09/11/2012 06:15:25 UPS: The battery is now installed.
09/11/2012 06:14:33 UPS: The battery is not installed properly.
09/11/2012 06:14:16 UPS: The battery is now installed.
09/10/2012 16:30:26 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:27:26 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:26:15 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:22:28 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:22:24 UPS: No longer in bypass.
09/10/2012 16:22:12 UPS: A discharged battery condition no longer exists.
09/10/2012 16:22:11 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:21:31 UPS: Synchronized command aborted.
09/10/2012 16:18:58 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:10:21 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:10:18 UPS: No longer in bypass.
09/10/2012 16:09:42 UPS: A discharged battery condition no longer exists.
09/10/2012 16:09:41 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:03:34 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:57:08 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:37:50 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:33:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:29:52 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:26:51 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:24:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:20:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:16:07 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:13:05 UPS: The battery is not installed properly.
09/10/2012 15:12:47 UPS: The battery is now installed.
09/10/2012 15:11:36 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:11:24 UPS: The battery is not installed properly.
09/10/2012 15:11:04 UPS: The battery is now installed.
09/10/2012 15:10:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:09:57 UPS: The battery is not installed properly.
09/10/2012 15:09:40 UPS: The battery is now installed.
09/10/2012 15:09:05 UPS: The battery is not installed properly.
09/10/2012 15:08:32 UPS: The battery is now installed.
09/10/2012 15:07:05 UPS: The battery is not installed properly.
09/10/2012 15:06:49 UPS: The battery is now installed.
09/10/2012 15:06:04 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:05:41 UPS: The battery is not installed properly.
09/10/2012 15:05:06 UPS: The battery is now installed.
09/10/2012 15:02:33 UPS: The battery is not installed properly.
09/10/2012 15:02:00 UPS: The battery is now installed.
09/10/2012 15:00:16 UPS: The battery is not installed properly.
09/10/2012 15:00:00 UPS: The battery is now installed.
09/10/2012 14:59:42 UPS: The battery is not installed properly.
09/10/2012 14:59:25 UPS: The battery is now installed.
09/10/2012 14:59:08 UPS: The battery is not installed properly.
09/10/2012 14:58:51 UPS: The battery is now installed.
09/10/2012 14:58:34 UPS: The battery is not installed properly.
09/10/2012 14:58:18 UPS: The battery is now installed.
09/10/2012 14:58:01 UPS: The battery is not installed properly.
09/10/2012 14:57:42 UPS: The battery is now installed.
09/10/2012 14:56:36 UPS: The battery is not installed properly.
09/10/2012 14:56:18 UPS: The battery is now installed.
09/10/2012 14:55:45 UPS: The battery is not installed properly.
09/10/2012 14:55:09 UPS: The battery is now installed.
09/10/2012 14:54:02 UPS: The battery is not installed properly.
09/10/2012 14:53:44 UPS: The battery is now installed.
09/10/2012 11:33:31 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:28:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:27:20 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:24:20 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:13:38 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:10:13 System: Configuration change. System location.
09/10/2012 11:10:13 System: Configuration change. System contact.
09/10/2012 11:10:12 System: Configuration change. System name.
09/10/2012 11:02:02 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:01:08 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:55:42 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:42:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:35:17 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:31:18 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:27:19 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:22:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:12:28 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:15:44 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:44 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:30 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:08:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:00:27 UPS: The battery is not installed properly.
09/10/2012 09:00:08 UPS: The battery is now installed.
09/10/2012 08:59:51 UPS: The battery is not installed properly.
09/10/2012 08:58:44 UPS: The battery is now installed.
09/10/2012 08:58:09 UPS: The battery is not installed properly.
09/10/2012 08:55:54 UPS: The battery is now installed.
09/10/2012 08:55:37 UPS: The battery is not installed properly.
09/10/2012 08:54:10 UPS: The battery is now installed.
09/10/2012 08:53:55 UPS: The battery is not installed properly.
09/10/2012 08:53:02 UPS: The battery is now installed.
09/10/2012 08:52:45 UPS: The battery is not installed properly.
09/10/2012 08:52:29 UPS: The battery is now installed.
09/10/2012 08:51:38 UPS: The battery is not installed properly.
09/10/2012 08:51:20 UPS: The battery is now installed.
09/10/2012 08:50:28 UPS: The battery is not installed properly.
09/10/2012 08:50:12 UPS: The battery is now installed.
09/10/2012 08:49:54 UPS: The battery is not installed properly.
09/10/2012 08:49:38 UPS: The battery is now installed.
09/10/2012 08:48:28 UPS: The battery is not installed properly.
09/10/2012 08:48:12 UPS: The battery is now installed.
09/09/2012 14:02:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:54:45 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:19:49 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:16:27 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:07:39 UPS: The battery is not installed properly.
09/09/2012 13:07:07 UPS: Self-Test Failed
09/09/2012 13:06:53 UPS: The output power is now turned on.
09/09/2012 13:06:53 UPS: The battery is now installed.
09/09/2012 13:06:51 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/09/2012 13:06:22 UPS: The battery is not installed properly.
09/09/2012 13:06:04 UPS: The output power is turned off.
09/09/2012 13:05:40 UPS: Self-Test Failed
09/09/2012 13:05:29 UPS: The output power is now turned on.
09/09/2012 13:05:27 UPS: The battery is now installed.
09/09/2012 13:05:25 UPS: At least one faulty battery exists.
09/09/2012 13:05:24 UPS: The output power is turned off.
09/09/2012 13:05:23 UPS: Synchronized UPS failed to complete the command.
09/09/2012 13:04:47 UPS: Started a reboot process.
09/09/2012 12:50:35 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:42:47 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by Web user '' from .11.
09/09/2012 12:42:46 UPS: Synchronized command aborted.
09/09/2012 12:40:24 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:33:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:30:24 System: Event Log cleared.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

is it the red LED with an X in a box or just a light with a red X?

do you have the logs for the network management card available?

instructions on downloading logs are available in knowledge base FA156131 @ http://www.apc.com/site/support/index.cfm/faq/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:35 AM . Last Modified: ‎2024-03-13 01:41 AM

yes the red LED is an X in the box flashing every 2second for long time and suddenly the battery stop the beep and the red LED light turned off for 10 or 15 second and i can see the charging level 2 green LED light for 10 second only and battery come back again to beep and the red LED ( x in the box ) come back again.

battery charge now is 32% two green led only

this is the log file


Date Time Event
Date Time Event
09/11/2012 09:25:27 UPS: The battery is not installed properly.
09/11/2012 09:25:11 UPS: The battery is now installed.
09/11/2012 09:24:54 UPS: The battery is not installed properly.
09/11/2012 09:24:36 UPS: The battery is now installed.
09/11/2012 09:23:47 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:21:04 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:17:10 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:15:31 UPS: The battery is not installed properly.
09/11/2012 09:15:13 UPS: The battery is now installed.
09/11/2012 09:14:21 UPS: The battery is not installed properly.
09/11/2012 09:13:47 UPS: The battery is now installed.
09/11/2012 09:10:41 UPS: The battery is not installed properly.
09/11/2012 09:10:23 UPS: The battery is now installed.
09/11/2012 09:04:58 UPS: The battery is not installed properly.
09/11/2012 09:04:41 UPS: The battery is now installed.
09/11/2012 08:59:17 UPS: The battery is not installed properly.
09/11/2012 08:59:00 UPS: The battery is now installed.
09/11/2012 08:58:25 UPS: The battery is not installed properly.
09/11/2012 08:58:09 UPS: The battery is now installed.
09/11/2012 08:57:53 UPS: The battery is not installed properly.
09/11/2012 08:57:35 UPS: The battery is now installed.
09/11/2012 08:55:52 UPS: The battery is not installed properly.
09/11/2012 08:55:35 UPS: The battery is now installed.
09/11/2012 08:54:44 UPS: The battery is not installed properly.
09/11/2012 08:54:27 UPS: The battery is now installed.
09/11/2012 08:53:02 UPS: The battery is not installed properly.
09/11/2012 08:52:43 UPS: The battery is now installed.
09/11/2012 08:26:43 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:23:14 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:19:09 UPS: The battery is not installed properly.
09/11/2012 08:18:53 UPS: The battery is now installed.
09/11/2012 07:33:04 UPS: The battery is not installed properly.
09/11/2012 07:32:46 UPS: The battery is now installed.
09/11/2012 07:31:03 UPS: The battery is not installed properly.
09/11/2012 07:30:48 UPS: The battery is now installed.
09/11/2012 07:29:22 UPS: The battery is not installed properly.
09/11/2012 07:29:04 UPS: The battery is now installed.
09/11/2012 07:28:47 UPS: The battery is not installed properly.
09/11/2012 07:28:14 UPS: The battery is now installed.
09/11/2012 07:27:22 UPS: The battery is not installed properly.
09/11/2012 07:27:05 UPS: The battery is now installed.
09/11/2012 07:22:33 UPS: The battery is not installed properly.
09/11/2012 07:21:59 UPS: The battery is now installed.
09/11/2012 07:17:26 UPS: The battery is not installed properly.
09/11/2012 07:17:07 UPS: The battery is now installed.
09/11/2012 07:15:59 UPS: The battery is not installed properly.
09/11/2012 07:15:43 UPS: The battery is now installed.
09/11/2012 07:15:26 UPS: The battery is not installed properly.
09/11/2012 07:14:51 UPS: The battery is now installed.
09/11/2012 07:14:34 UPS: The battery is not installed properly.
09/11/2012 07:14:18 UPS: The battery is now installed.
09/11/2012 07:13:26 UPS: The battery is not installed properly.
09/11/2012 07:13:08 UPS: The battery is now installed.
09/11/2012 07:12:17 UPS: The battery is not installed properly.
09/11/2012 07:12:01 UPS: The battery is now installed.
09/11/2012 07:07:10 UPS: The battery is not installed properly.
09/11/2012 07:06:54 UPS: The battery is now installed.
09/11/2012 07:05:11 UPS: The battery is not installed properly.
09/11/2012 07:04:21 UPS: The battery is now installed.
09/11/2012 07:03:29 UPS: The battery is not installed properly.
09/11/2012 07:02:20 UPS: The battery is now installed.
09/11/2012 07:02:03 UPS: The battery is not installed properly.
09/11/2012 07:01:45 UPS: The battery is now installed.
09/11/2012 06:59:47 UPS: The battery is not installed properly.
09/11/2012 06:59:30 UPS: The battery is now installed.
09/11/2012 06:58:37 UPS: The battery is not installed properly.
09/11/2012 06:58:22 UPS: The battery is now installed.
09/11/2012 06:56:39 UPS: The battery is not installed properly.
09/11/2012 06:56:04 UPS: The battery is now installed.
09/11/2012 06:54:56 UPS: The battery is not installed properly.
09/11/2012 06:54:40 UPS: The battery is now installed.
09/11/2012 06:54:06 UPS: The battery is not installed properly.
09/11/2012 06:52:24 UPS: The battery is now installed.
09/11/2012 06:50:57 UPS: The battery is not installed properly.
09/11/2012 06:50:08 UPS: The battery is now installed.
09/11/2012 06:49:51 UPS: The battery is not installed properly.
09/11/2012 06:49:33 UPS: The battery is now installed.
09/11/2012 06:47:15 UPS: The battery is not installed properly.
09/11/2012 06:44:58 UPS: The battery is now installed.
09/11/2012 06:44:08 UPS: The battery is not installed properly.
09/11/2012 06:43:52 UPS: The battery is now installed.
09/11/2012 06:43:18 UPS: The battery is not installed properly.
09/11/2012 06:42:59 UPS: The battery is now installed.
09/11/2012 06:42:42 UPS: The battery is not installed properly.
09/11/2012 06:42:26 UPS: The battery is now installed.
09/11/2012 06:42:09 UPS: The battery is not installed properly.
09/11/2012 06:41:51 UPS: The battery is now installed.
09/11/2012 06:40:09 UPS: The battery is not installed properly.
09/11/2012 06:39:52 UPS: The battery is now installed.
09/11/2012 06:39:35 UPS: The battery is not installed properly.
09/11/2012 06:39:18 UPS: The battery is now installed.
09/11/2012 06:38:26 UPS: The battery is not installed properly.
09/11/2012 06:38:11 UPS: The battery is now installed.
09/11/2012 06:37:01 UPS: The battery is not installed properly.
09/11/2012 06:36:11 UPS: The battery is now installed.
09/11/2012 06:33:37 UPS: The battery is not installed properly.
09/11/2012 06:33:03 UPS: The battery is now installed.
09/11/2012 06:31:55 UPS: The battery is not installed properly.
09/11/2012 06:31:48 UPS: A discharged battery condition no longer exists.
09/11/2012 06:31:20 UPS: The battery is now installed.
09/11/2012 06:31:03 UPS: The battery is not installed properly.
09/11/2012 06:30:47 UPS: The battery is now installed.
09/11/2012 06:29:21 UPS: The battery is not installed properly.
09/11/2012 06:29:04 UPS: The battery is now installed.
09/11/2012 06:26:30 UPS: The battery is not installed properly.
09/11/2012 06:26:13 UPS: The battery is now installed.
09/11/2012 06:25:38 UPS: The battery is not installed properly.
09/11/2012 06:25:05 UPS: The battery is now installed.
09/11/2012 06:21:05 UPS: The battery is not installed properly.
09/11/2012 06:20:15 UPS: The battery is now installed.
09/11/2012 06:19:06 UPS: The battery is not installed properly.
09/11/2012 06:18:49 UPS: The battery is now installed.
09/11/2012 06:18:33 UPS: The battery is not installed properly.
09/11/2012 06:17:42 UPS: The battery is now installed.
09/11/2012 06:16:16 UPS: The battery is not installed properly.
09/11/2012 06:15:59 UPS: The battery is now installed.
09/11/2012 06:15:42 UPS: The battery is not installed properly.
09/11/2012 06:15:25 UPS: The battery is now installed.
09/11/2012 06:14:33 UPS: The battery is not installed properly.
09/11/2012 06:14:16 UPS: The battery is now installed.
09/10/2012 16:30:26 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:27:26 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:26:15 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:22:28 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:22:24 UPS: No longer in bypass.
09/10/2012 16:22:12 UPS: A discharged battery condition no longer exists.
09/10/2012 16:22:11 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:21:31 UPS: Synchronized command aborted.
09/10/2012 16:18:58 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:10:21 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:10:18 UPS: No longer in bypass.
09/10/2012 16:09:42 UPS: A discharged battery condition no longer exists.
09/10/2012 16:09:41 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:03:34 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:57:08 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:37:50 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:33:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:29:52 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:26:51 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:24:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:20:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:16:07 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:13:05 UPS: The battery is not installed properly.
09/10/2012 15:12:47 UPS: The battery is now installed.
09/10/2012 15:11:36 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:11:24 UPS: The battery is not installed properly.
09/10/2012 15:11:04 UPS: The battery is now installed.
09/10/2012 15:10:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:09:57 UPS: The battery is not installed properly.
09/10/2012 15:09:40 UPS: The battery is now installed.
09/10/2012 15:09:05 UPS: The battery is not installed properly.
09/10/2012 15:08:32 UPS: The battery is now installed.
09/10/2012 15:07:05 UPS: The battery is not installed properly.
09/10/2012 15:06:49 UPS: The battery is now installed.
09/10/2012 15:06:04 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:05:41 UPS: The battery is not installed properly.
09/10/2012 15:05:06 UPS: The battery is now installed.
09/10/2012 15:02:33 UPS: The battery is not installed properly.
09/10/2012 15:02:00 UPS: The battery is now installed.
09/10/2012 15:00:16 UPS: The battery is not installed properly.
09/10/2012 15:00:00 UPS: The battery is now installed.
09/10/2012 14:59:42 UPS: The battery is not installed properly.
09/10/2012 14:59:25 UPS: The battery is now installed.
09/10/2012 14:59:08 UPS: The battery is not installed properly.
09/10/2012 14:58:51 UPS: The battery is now installed.
09/10/2012 14:58:34 UPS: The battery is not installed properly.
09/10/2012 14:58:18 UPS: The battery is now installed.
09/10/2012 14:58:01 UPS: The battery is not installed properly.
09/10/2012 14:57:42 UPS: The battery is now installed.
09/10/2012 14:56:36 UPS: The battery is not installed properly.
09/10/2012 14:56:18 UPS: The battery is now installed.
09/10/2012 14:55:45 UPS: The battery is not installed properly.
09/10/2012 14:55:09 UPS: The battery is now installed.
09/10/2012 14:54:02 UPS: The battery is not installed properly.
09/10/2012 14:53:44 UPS: The battery is now installed.
09/10/2012 11:33:31 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:28:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:27:20 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:24:20 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:13:38 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:10:13 System: Configuration change. System location.
09/10/2012 11:10:13 System: Configuration change. System contact.
09/10/2012 11:10:12 System: Configuration change. System name.
09/10/2012 11:02:02 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:01:08 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:55:42 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:42:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:35:17 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:31:18 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:27:19 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:22:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:12:28 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:15:44 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:44 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:30 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:08:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:00:27 UPS: The battery is not installed properly.
09/10/2012 09:00:08 UPS: The battery is now installed.
09/10/2012 08:59:51 UPS: The battery is not installed properly.
09/10/2012 08:58:44 UPS: The battery is now installed.
09/10/2012 08:58:09 UPS: The battery is not installed properly.
09/10/2012 08:55:54 UPS: The battery is now installed.
09/10/2012 08:55:37 UPS: The battery is not installed properly.
09/10/2012 08:54:10 UPS: The battery is now installed.
09/10/2012 08:53:55 UPS: The battery is not installed properly.
09/10/2012 08:53:02 UPS: The battery is now installed.
09/10/2012 08:52:45 UPS: The battery is not installed properly.
09/10/2012 08:52:29 UPS: The battery is now installed.
09/10/2012 08:51:38 UPS: The battery is not installed properly.
09/10/2012 08:51:20 UPS: The battery is now installed.
09/10/2012 08:50:28 UPS: The battery is not installed properly.
09/10/2012 08:50:12 UPS: The battery is now installed.
09/10/2012 08:49:54 UPS: The battery is not installed properly.
09/10/2012 08:49:38 UPS: The battery is now installed.
09/10/2012 08:48:28 UPS: The battery is not installed properly.
09/10/2012 08:48:12 UPS: The battery is now installed.
09/09/2012 14:02:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:54:45 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:19:49 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:16:27 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:07:39 UPS: The battery is not installed properly.
09/09/2012 13:07:07 UPS: Self-Test Failed
09/09/2012 13:06:53 UPS: The output power is now turned on.
09/09/2012 13:06:53 UPS: The battery is now installed.
09/09/2012 13:06:51 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/09/2012 13:06:22 UPS: The battery is not installed properly.
09/09/2012 13:06:04 UPS: The output power is turned off.
09/09/2012 13:05:40 UPS: Self-Test Failed
09/09/2012 13:05:29 UPS: The output power is now turned on.
09/09/2012 13:05:27 UPS: The battery is now installed.
09/09/2012 13:05:25 UPS: At least one faulty battery exists.
09/09/2012 13:05:24 UPS: The output power is turned off.
09/09/2012 13:05:23 UPS: Synchronized UPS failed to complete the command.
09/09/2012 13:04:47 UPS: Started a reboot process.
09/09/2012 12:50:35 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:42:47 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by Web user '' from 4.30.8.11.
09/09/2012 12:42:46 UPS: Synchronized command aborted.
09/09/2012 12:40:24 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:33:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:30:24 System: Event Log cleared.

Message was edited by: crownjeddah

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:41 AM

i asked someone more familiar with the UPS and they indicated that if it were them, they'd try replacing the batteries first even though the voltage is good.

before i suggest you actually pursue that though, can you please let me know the serial number of the UPS please?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:41 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:41 AM

hi

thank you for your reply

this is the information for the UPS


Model: Smart-UPS RT 10000 RM XL
Position: RACK
Serial Number: IS1038000600
Firmware Revision: 476.18.W
Manufacture Date: 09/13/10

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

can you let me know where this unit is installed? the symptoms indicate bad batteries but 2 years is on the low side for battery life. if its in a warmer closet or rack, this could also be the case or if there are a lot of power issues in the area where the batteries are used more frequently. you could also try to do a self test and see what happens (you can hold down the test button on the front of the UPS) but depending on the issue, it could potentially turn the output of the UPS off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

0 Likes
0
1054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:36 AM . Last Modified: ‎2024-03-13 01:40 AM

this is the log file

Date Time Event
Date Time Event
09/11/2012 09:25:27 UPS: The battery is not installed properly.
09/11/2012 09:25:11 UPS: The battery is now installed.
09/11/2012 09:24:54 UPS: The battery is not installed properly.
09/11/2012 09:24:36 UPS: The battery is now installed.
09/11/2012 09:23:47 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:21:04 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:17:10 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 09:15:31 UPS: The battery is not installed properly.
09/11/2012 09:15:13 UPS: The battery is now installed.
09/11/2012 09:14:21 UPS: The battery is not installed properly.
09/11/2012 09:13:47 UPS: The battery is now installed.
09/11/2012 09:10:41 UPS: The battery is not installed properly.
09/11/2012 09:10:23 UPS: The battery is now installed.
09/11/2012 09:04:58 UPS: The battery is not installed properly.
09/11/2012 09:04:41 UPS: The battery is now installed.
09/11/2012 08:59:17 UPS: The battery is not installed properly.
09/11/2012 08:59:00 UPS: The battery is now installed.
09/11/2012 08:58:25 UPS: The battery is not installed properly.
09/11/2012 08:58:09 UPS: The battery is now installed.
09/11/2012 08:57:53 UPS: The battery is not installed properly.
09/11/2012 08:57:35 UPS: The battery is now installed.
09/11/2012 08:55:52 UPS: The battery is not installed properly.
09/11/2012 08:55:35 UPS: The battery is now installed.
09/11/2012 08:54:44 UPS: The battery is not installed properly.
09/11/2012 08:54:27 UPS: The battery is now installed.
09/11/2012 08:53:02 UPS: The battery is not installed properly.
09/11/2012 08:52:43 UPS: The battery is now installed.
09/11/2012 08:26:43 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:23:14 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/11/2012 08:19:09 UPS: The battery is not installed properly.
09/11/2012 08:18:53 UPS: The battery is now installed.
09/11/2012 07:33:04 UPS: The battery is not installed properly.
09/11/2012 07:32:46 UPS: The battery is now installed.
09/11/2012 07:31:03 UPS: The battery is not installed properly.
09/11/2012 07:30:48 UPS: The battery is now installed.
09/11/2012 07:29:22 UPS: The battery is not installed properly.
09/11/2012 07:29:04 UPS: The battery is now installed.
09/11/2012 07:28:47 UPS: The battery is not installed properly.
09/11/2012 07:28:14 UPS: The battery is now installed.
09/11/2012 07:27:22 UPS: The battery is not installed properly.
09/11/2012 07:27:05 UPS: The battery is now installed.
09/11/2012 07:22:33 UPS: The battery is not installed properly.
09/11/2012 07:21:59 UPS: The battery is now installed.
09/11/2012 07:17:26 UPS: The battery is not installed properly.
09/11/2012 07:17:07 UPS: The battery is now installed.
09/11/2012 07:15:59 UPS: The battery is not installed properly.
09/11/2012 07:15:43 UPS: The battery is now installed.
09/11/2012 07:15:26 UPS: The battery is not installed properly.
09/11/2012 07:14:51 UPS: The battery is now installed.
09/11/2012 07:14:34 UPS: The battery is not installed properly.
09/11/2012 07:14:18 UPS: The battery is now installed.
09/11/2012 07:13:26 UPS: The battery is not installed properly.
09/11/2012 07:13:08 UPS: The battery is now installed.
09/11/2012 07:12:17 UPS: The battery is not installed properly.
09/11/2012 07:12:01 UPS: The battery is now installed.
09/11/2012 07:07:10 UPS: The battery is not installed properly.
09/11/2012 07:06:54 UPS: The battery is now installed.
09/11/2012 07:05:11 UPS: The battery is not installed properly.
09/11/2012 07:04:21 UPS: The battery is now installed.
09/11/2012 07:03:29 UPS: The battery is not installed properly.
09/11/2012 07:02:20 UPS: The battery is now installed.
09/11/2012 07:02:03 UPS: The battery is not installed properly.
09/11/2012 07:01:45 UPS: The battery is now installed.
09/11/2012 06:59:47 UPS: The battery is not installed properly.
09/11/2012 06:59:30 UPS: The battery is now installed.
09/11/2012 06:58:37 UPS: The battery is not installed properly.
09/11/2012 06:58:22 UPS: The battery is now installed.
09/11/2012 06:56:39 UPS: The battery is not installed properly.
09/11/2012 06:56:04 UPS: The battery is now installed.
09/11/2012 06:54:56 UPS: The battery is not installed properly.
09/11/2012 06:54:40 UPS: The battery is now installed.
09/11/2012 06:54:06 UPS: The battery is not installed properly.
09/11/2012 06:52:24 UPS: The battery is now installed.
09/11/2012 06:50:57 UPS: The battery is not installed properly.
09/11/2012 06:50:08 UPS: The battery is now installed.
09/11/2012 06:49:51 UPS: The battery is not installed properly.
09/11/2012 06:49:33 UPS: The battery is now installed.
09/11/2012 06:47:15 UPS: The battery is not installed properly.
09/11/2012 06:44:58 UPS: The battery is now installed.
09/11/2012 06:44:08 UPS: The battery is not installed properly.
09/11/2012 06:43:52 UPS: The battery is now installed.
09/11/2012 06:43:18 UPS: The battery is not installed properly.
09/11/2012 06:42:59 UPS: The battery is now installed.
09/11/2012 06:42:42 UPS: The battery is not installed properly.
09/11/2012 06:42:26 UPS: The battery is now installed.
09/11/2012 06:42:09 UPS: The battery is not installed properly.
09/11/2012 06:41:51 UPS: The battery is now installed.
09/11/2012 06:40:09 UPS: The battery is not installed properly.
09/11/2012 06:39:52 UPS: The battery is now installed.
09/11/2012 06:39:35 UPS: The battery is not installed properly.
09/11/2012 06:39:18 UPS: The battery is now installed.
09/11/2012 06:38:26 UPS: The battery is not installed properly.
09/11/2012 06:38:11 UPS: The battery is now installed.
09/11/2012 06:37:01 UPS: The battery is not installed properly.
09/11/2012 06:36:11 UPS: The battery is now installed.
09/11/2012 06:33:37 UPS: The battery is not installed properly.
09/11/2012 06:33:03 UPS: The battery is now installed.
09/11/2012 06:31:55 UPS: The battery is not installed properly.
09/11/2012 06:31:48 UPS: A discharged battery condition no longer exists.
09/11/2012 06:31:20 UPS: The battery is now installed.
09/11/2012 06:31:03 UPS: The battery is not installed properly.
09/11/2012 06:30:47 UPS: The battery is now installed.
09/11/2012 06:29:21 UPS: The battery is not installed properly.
09/11/2012 06:29:04 UPS: The battery is now installed.
09/11/2012 06:26:30 UPS: The battery is not installed properly.
09/11/2012 06:26:13 UPS: The battery is now installed.
09/11/2012 06:25:38 UPS: The battery is not installed properly.
09/11/2012 06:25:05 UPS: The battery is now installed.
09/11/2012 06:21:05 UPS: The battery is not installed properly.
09/11/2012 06:20:15 UPS: The battery is now installed.
09/11/2012 06:19:06 UPS: The battery is not installed properly.
09/11/2012 06:18:49 UPS: The battery is now installed.
09/11/2012 06:18:33 UPS: The battery is not installed properly.
09/11/2012 06:17:42 UPS: The battery is now installed.
09/11/2012 06:16:16 UPS: The battery is not installed properly.
09/11/2012 06:15:59 UPS: The battery is now installed.
09/11/2012 06:15:42 UPS: The battery is not installed properly.
09/11/2012 06:15:25 UPS: The battery is now installed.
09/11/2012 06:14:33 UPS: The battery is not installed properly.
09/11/2012 06:14:16 UPS: The battery is now installed.
09/10/2012 16:30:26 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:27:26 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:26:15 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:22:28 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:22:24 UPS: No longer in bypass.
09/10/2012 16:22:12 UPS: A discharged battery condition no longer exists.
09/10/2012 16:22:11 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:21:31 UPS: Synchronized command aborted.
09/10/2012 16:18:58 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 16:10:21 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/10/2012 16:10:18 UPS: No longer in bypass.
09/10/2012 16:09:42 UPS: A discharged battery condition no longer exists.
09/10/2012 16:09:41 UPS: In bypass in response to the bypass switch at the UPS, typically for maintenance.
09/10/2012 16:03:34 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:57:08 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:37:50 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:33:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:29:52 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:26:51 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:24:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:20:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:16:07 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:13:05 UPS: The battery is not installed properly.
09/10/2012 15:12:47 UPS: The battery is now installed.
09/10/2012 15:11:36 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:11:24 UPS: The battery is not installed properly.
09/10/2012 15:11:04 UPS: The battery is now installed.
09/10/2012 15:10:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:09:57 UPS: The battery is not installed properly.
09/10/2012 15:09:40 UPS: The battery is now installed.
09/10/2012 15:09:05 UPS: The battery is not installed properly.
09/10/2012 15:08:32 UPS: The battery is now installed.
09/10/2012 15:07:05 UPS: The battery is not installed properly.
09/10/2012 15:06:49 UPS: The battery is now installed.
09/10/2012 15:06:04 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 15:05:41 UPS: The battery is not installed properly.
09/10/2012 15:05:06 UPS: The battery is now installed.
09/10/2012 15:02:33 UPS: The battery is not installed properly.
09/10/2012 15:02:00 UPS: The battery is now installed.
09/10/2012 15:00:16 UPS: The battery is not installed properly.
09/10/2012 15:00:00 UPS: The battery is now installed.
09/10/2012 14:59:42 UPS: The battery is not installed properly.
09/10/2012 14:59:25 UPS: The battery is now installed.
09/10/2012 14:59:08 UPS: The battery is not installed properly.
09/10/2012 14:58:51 UPS: The battery is now installed.
09/10/2012 14:58:34 UPS: The battery is not installed properly.
09/10/2012 14:58:18 UPS: The battery is now installed.
09/10/2012 14:58:01 UPS: The battery is not installed properly.
09/10/2012 14:57:42 UPS: The battery is now installed.
09/10/2012 14:56:36 UPS: The battery is not installed properly.
09/10/2012 14:56:18 UPS: The battery is now installed.
09/10/2012 14:55:45 UPS: The battery is not installed properly.
09/10/2012 14:55:09 UPS: The battery is now installed.
09/10/2012 14:54:02 UPS: The battery is not installed properly.
09/10/2012 14:53:44 UPS: The battery is now installed.
09/10/2012 11:33:31 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:28:00 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:27:20 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:24:20 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:13:38 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:10:13 System: Configuration change. System location.
09/10/2012 11:10:13 System: Configuration change. System contact.
09/10/2012 11:10:12 System: Configuration change. System name.
09/10/2012 11:02:02 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 11:01:08 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:55:42 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:42:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:35:17 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:31:18 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:27:19 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:22:40 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 10:12:28 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:15:44 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:44 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:12:30 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:08:12 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/10/2012 09:00:27 UPS: The battery is not installed properly.
09/10/2012 09:00:08 UPS: The battery is now installed.
09/10/2012 08:59:51 UPS: The battery is not installed properly.
09/10/2012 08:58:44 UPS: The battery is now installed.
09/10/2012 08:58:09 UPS: The battery is not installed properly.
09/10/2012 08:55:54 UPS: The battery is now installed.
09/10/2012 08:55:37 UPS: The battery is not installed properly.
09/10/2012 08:54:10 UPS: The battery is now installed.
09/10/2012 08:53:55 UPS: The battery is not installed properly.
09/10/2012 08:53:02 UPS: The battery is now installed.
09/10/2012 08:52:45 UPS: The battery is not installed properly.
09/10/2012 08:52:29 UPS: The battery is now installed.
09/10/2012 08:51:38 UPS: The battery is not installed properly.
09/10/2012 08:51:20 UPS: The battery is now installed.
09/10/2012 08:50:28 UPS: The battery is not installed properly.
09/10/2012 08:50:12 UPS: The battery is now installed.
09/10/2012 08:49:54 UPS: The battery is not installed properly.
09/10/2012 08:49:38 UPS: The battery is now installed.
09/10/2012 08:48:28 UPS: The battery is not installed properly.
09/10/2012 08:48:12 UPS: The battery is now installed.
09/09/2012 14:02:33 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:54:45 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:19:49 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:16:27 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 13:07:39 UPS: The battery is not installed properly.
09/09/2012 13:07:07 UPS: Self-Test Failed
09/09/2012 13:06:53 UPS: The output power is now turned on.
09/09/2012 13:06:53 UPS: The battery is now installed.
09/09/2012 13:06:51 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09/09/2012 13:06:22 UPS: The battery is not installed properly.
09/09/2012 13:06:04 UPS: The output power is turned off.
09/09/2012 13:05:40 UPS: Self-Test Failed
09/09/2012 13:05:29 UPS: The output power is now turned on.
09/09/2012 13:05:27 UPS: The battery is now installed.
09/09/2012 13:05:25 UPS: At least one faulty battery exists.
09/09/2012 13:05:24 UPS: The output power is turned off.
09/09/2012 13:05:23 UPS: Synchronized UPS failed to complete the command.
09/09/2012 13:04:47 UPS: Started a reboot process.
09/09/2012 12:50:35 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:42:47 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by Web user '' from .11.
09/09/2012 12:42:46 UPS: Synchronized command aborted.
09/09/2012 12:40:24 System: Web user 'apc' logged in from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:33:32 System: Web user 'apc' logged out from 4.30.8.11 [nsa430-000001.crowncork.com].
09/09/2012 12:30:24 System: Event Log cleared.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore